Okay to not install expansion tank for domestic?
sunlight33
Member Posts: 378
If there is no backflow preventer installed on city water, is there any benefit to install an expansion tank (for indirect water heater)? I have been living in my house for several years and recently I have a chance to redo the plumbing so I am wondering if I should take this opportunity to add a tank.
0
Comments
-
Add the tank. Eventually you’ll get a back flow preventer.0
-
Or if you add a recir system for DHW you would need a check valve on the cold.
I would add a tee for future connection of the tank. Even a tee with a valve so you would not have to drain down to add or change tank.0 -
Why add the tank?
Install the back flow preventer, do not forget that probably is a code item and will need a plumber with a lic. or certification.
Also do what Jughe said, future also find ways to jump up and and become now.
jakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
What @JUGHNE said.
I wouldn't add a tank unless you have to. Just another thing to have to maintain and eventually fail3 -
Yeah I will probably add a tee with a threaded cap.0
-
0
-
50 psi0
-
Hi, with that pressure, I see no reason why a reducer or other backflow device will be needed any time soon. Simple is good. I’d skip the expansion tank.
Yours,,Larry0 -
It's not uncommon for the water utility to upgrade the meter or meter yoke to a BFD type, then you will see relief valves start seeping or pop off.
Install a stainless or bag type expansion tank and it will probably outlast the tank.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I wouldn't add anything that's not needed.
Maybe they will require a BFP, maybe they won't and if they do no one knows how many decades from now it could be.
If it does happen do what's required at the time and you'll have a nice new tank then.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements