At least the Hartford Loop looks good
GW
GW Member Posts: 5,184
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    Steamhead Member Posts: 18,625
    And what a cute little main vent!
    Consulting
    GW
    Hey -- at least they used both outlets...
    GW
    mattmia2 Member Posts: 17,209
    one for water, one for steam...
    CanuckerGW
    EBEBRATT-Ed Member Posts: 20,394
    @GW
    Repiping or a new boiler?
    DrewM
  • GW
    Ed no we installed a new mini ac, new rad valve and a new feeder for the boiler
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • Gordo
    Gordo Member Posts: 857
    @GW: What feeder did you use?
  • GW
    edited May 2021
    hydrolevel vxt-24
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    Gordo
    EdTheHeaterMan Member Posts: 12,448
    edited May 2021
    Where is the Circulator pump? Since one side is a wet riser and the other side is a steam riser?
    Should you "Pump Away" from the steam riser?
    Good thing they left that loop in the piping for the vent connector to fit around all that Iron Pipe.
  • GW
    Ok now I’m not sure if you’re kidding or not, it’s just a poorly piped steamer!
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,323
    It may actually steam pretty good, If its small enough the velocity in the 2- 2inch risers may be low enough to allow the water to fall back into the boiler. I''ll admit to doing this once with a little 112,000 input Dunkirk with 2- 2 1/2 inch risers in a counterflow system for someone with no money to do all the extra piping. Did the job, despite not being right.
    ethicalpaulGW
