Extreme water hammer
iPipefitter
Member Posts: 15
I work as a pipefitter, still rather new to my trade. Trying to learn all I can to become the best I can be. I been having issues with extreme water hammer. I noticed the some of the pipes aren't insulated as there was a leak that required me to tear of the insulation in order to fix the leak. The traps seem to be good, tested them with a ultrasound device, everything is pitched correctly, there does seem to be too long of a nipple in the in the Hartford loop. I fixed the nipple issue to meet common standards, however, it's still pretty bad. Could the lack of insulation really contribute that much to the cause of the water hammer? I know it loses quite a bit of heat due to lack of insulation, or do you all think that there could be another underlying issue? My thought is that the lack of insulation is causing more condensate than they can handle but was wondering others opinions too.
Thank you.
Thank you.
0
Comments
-
pictures of the boiler and near boiler piping and anything else unusual would help. Is the water level in the site glass stable when it is steaming or does it bounce up and down a lot? Is the level in the system cold and while steaming drastically different? is it all 2 pipe? what is the pressure set at and what is the actual pressure?2
-
It would kind of be hard to take a picture of the boiler because I'm at a huge plant that has a power house with 4 huge boilers probably the size of a small house. It's a huge system that runs with 24" mains, maybe this is just a common issue with systems this large that cannot be fully prevented or contained. I was just thinking it was narrowed down to that specific unit heater.0
-
I can't really post pictures it's against my companies policy. I could try to check the pressures, and give you some more data, it's super high pressure steam with PRV's all over to reduce to lower pressure for the unit heaters and other various aspects of the plant.mattmia2 said:pictures of the boiler and near boiler piping and anything else unusual would help. Is the water level in the site glass stable when it is steaming or does it bounce up and down a lot? Is the level in the system cold and while steaming drastically different? is it all 2 pipe? what is the pressure set at and what is the actual pressure?
0 -
-
Yes, not having insulation will create excessive condensate and this can certainly cause water hammer.Retired and loving it.0
-
What is the boilers operating steam pressure steam, what size are the boilers, and where is the steam hammer happening, in the boiler room, out in the system, at the deaerator, where? Is this an old system or newer system? Is this a hospital, school or industrial building? Is the steam used for heating or processing or both? Much more information is needed for anyone to make even an educated guess as to what is causing the steam hammer. Where in the USA are you? Name the city. We need more information and pictures.0
-
@iPipefitter
On a job like that if all the pipe is pitched right and you getting water hammer the most likely reason is a bad trap(s).
You mentioned a unit heater is any equipment piped where it has to lift the condensate to an overhead return?0 -
I found some bad traps, replaced them and had the pipe re insulated and the issue stopped. Thank you for all your replies.EBEBRATT-Ed said:@iPipefitter
On a job like that if all the pipe is pitched right and you getting water hammer the most likely reason is a bad trap(s).
You mentioned a unit heater is any equipment piped where it has to lift the condensate to an overhead return?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements