control
Timmysledge
Member Posts: 6
Can someone tell me what this controls purpose is. It was connected at one point to a steam boiler that now is using a tekmar 264 control for a single stage steam boiler. Since it is a commercial building i assume this is why there using it for outdoor setpoint since they have a separate water heater.
0
Comments
-
Well, I see a time clock with 'building warm' & 'night setback' pointers, a mode switch with (presumably) 'A', 'B', 'C' (time clock), & 'D'; 'heating period' (on-time duration a la anticipator?); 'hold fire' (off time?); & what can only be a temperature sensor of some kind. Night setback, not outdoor reset.
Save it. While you can't adjust it with your phone, it almost certainly still works...
0 -
That's a VERY old boiler cycling control for a coal-fired boiler. The "Hold Fire/Refueler" function operated the coal stoker just long enough so that coal would be added to sustain the fire during mild weather.
You say they're using a Tekmar 264 now? Sure it's not a 269?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Definitely a 264.
Thanks for the information. The first that I have seen in Wisconsin.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements