Best TRV for Steam - 2 pipe system
Steamed2
Member Posts: 8
We are fitting a 44 unit condo with TRVs on every radiator -- does anyone have any recommendation which TRVs are the most durable for this type of application. Appreciate any thoughts on the matter...
0
Comments
-
Danfoss offers a whole line of steam TRV. If it is installed according to instructions, they last forever.
0 -
What is controlling the boiler?--NBC0
-
I have had pretty good luck with Danfoss0
-
Consider Macon from https://www.tunstall-inc.com/macon-controls/. Tunstall's knowledge and service is as good as it gets.Retired and loving it.0
-
Hi Steamed2! My name is Scott Malo and I am the Director of Energy Solutions for Tunstall Corporation. We would love to help you on your TRV project. Please feel free to call 413-862-7923 or email me at smalo@tunstall-inc.com and we can help!0
-
-
TRV's work very well on steam systems. We participate in many projects annually where TRV's are installed. Most often, these old radiators and convectors have a burned out hand valve and the tenants are using the window as the thermostat. Getting a TRV with a temperature limiting thermostat will get that overheated rad/conv under control. Done throughout the entire building and you will see some significant energy savings and a return to some tenant comfort.1
-
I live in a 25-unit apt. building from 1925. We have installed TRVs on almost all radiators, primarily Honeywell but with a few Danfoss. In my own apartment there are 7 rads; 5 H'well and 2 Danfoss. The H'wells with remote sensors have had to be replaced a couple of times. Never had a problem with the Danfoss.0
-
What turns on your boiler, Stuart? Is your system one pipe or two?—NBC0
-
Never heard of a problem with TRVs on two pipe steam when they're installed on all terminals. HHW is a different situation.0
-
I just wonder how to prevent the inside sensor of a building steam control from fighting with the TRV’s on the radiators.
Many hot water systems will rely on the outside temperature for control of the loop water temperature, and the TRV’s on the radiators can prevent any hotspots.
Maybe this is where a bit of vacuum can help with any imbalance, or heating response lag.—NBC0 -
Good question but generally TRVs don't care about steam pressure so long that there is some. Ideally 44 unit building has multiple boilers so one undersized boiler runs continuously. Setback can actually work with two pipe steam TRVs.nicholas bonham-carter said:
I just wonder how to prevent the inside sensor of a building steam control from fighting with the TRV’s on the radiators.
Many hot water systems will rely on the outside temperature for control of the loop water temperature, and the TRV’s on the radiators can prevent any hotspots.
Maybe this is where a bit of vacuum can help with any imbalance, or heating response lag.—NBC0 -
Just installing trvs may create additional problems. You should concentrate on finding good contractor, not trvs.Gennady Tsakh
Absolute Mechanical Co. Inc.1 -
This is our boiler -- it is a 2 piped steam system...
0 -
First of all, calculate the EDR of the radiation using one of the charts from somewhere here, and verify that it matches the square feet of steam rating of your boiler.
Next, check the traps, on the radiators, and any crossover traps for function,
Make sure the air can get out of the pipes quickly, through an adequate main vent, such as a Gorton #2, or a big mouth vent.
Choose your boiler control, which may be regulated by outdoor or indoor temperature, (sensor in the most exposed section of the building). I like indoor control for my 55 radiators, but others may be carrying a torch for Tekmar or Heatimer, outdoor control. Radiators near the indoor sensor, must NOT have TRV’s. My view of them is as a solution for an individual oversized radiator to reduce its heat, and not as a building control.—NBC0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements