Argo arm 3p shuts off when water comes to temp
Dan724
Member Posts: 9
in Oil Heating
I'm hoping for some guidance. I have a peerless boiler with coil. I had an issue with Argo control board and circulator pump short due to water damage.i have replaced the board and pump. However the board looses power when water comes to temp. I shut breaker after a while power comes back. Water comes to temp shuts off. Any archive would be appreciated.
0
Comments
-
-
Yes wired just like the original. How does the board take to rest0
-
0 -
Is priority switch 'on'? Also, what's hooked up to ZC/ZR? I assume they are on the same terminals as the aquastat but it's worth another look to see if ZC goes to ZC and ZR-ZR. Also that relay is de-energized when the boiler temp signals the low limit to fire the burner.
Type of equipment-make/model #? Make/model # of aquastat?There was an error rendering this rich post.
0 -
No priorty switch is not on. Yes confirmed zr and zc. Honeywell stat no model number I can see.. The board powers off when water hits temp. How long does it to rest. It took a while is there a time limit or can reset board?0
-
Honeywell triple aquastat relay. Type l8124a, c0
-
Peerless ec 03 100 wpct0
-
-
Hi James , yes I have confirmed 120 power to the board at the terminals0
-
Does anyone know how the electronic fuse auto shutoff works? How long till reset?0
-
Those low voltage t-stat wires look burnt. Whats the TT on the Honeywell connected to? Why are you not using the end switch on the Argo?0
-
If L (Black) on the Argo panel goes directly to L1 on the aquastat, then what's powering the aquastat? It looks like Hot, Neutral, ZR (Red) and ZC (Yellow) all come through the same conduit into the aquastat. Is there a splice or switch box between? Maybe a loose connection in the box. Hot or Neutral.
There is no timer or reset. The panel should be constantly powered. Circulator power is controlled by ZR,ZC.0 -
The electronic fuse should not be activated (open circuit) under normal operation. The amount of time it takes to reset will depend on the load that caused the fuse to trip. That said, do you believe the fuse is tripping? If so, have you checked to see if there is 24 V at the board where indicated by the red circle?
If you have 24V there then the fuse is not tripped. If you do not have 24V there then you need to find out why the 24 V circuit is overloaded.
How many zones total? I see 2 on the ARGO... is there one on the L8124 aquastat also for a total of 3 zones?
How many Circulator Pumps are there in your system? If you only have 2 circulators and 2 thermostats, then there should not be any wires connected to the T T terminals on the L8124 control. I believe that may be where you are getting your overcurrent that is tripping the ARGO electronic fuse.
According to the ARGO instructions, the circulators should not operate if the boiler L8124 control is below the minimum temperature to make DHW. This means the burner is operating.
The way I am reading your query, the burner stops because the boiler is up to temperature for DHW and the ARGO does not allow the heating zone circulators to operate. Did I get that right?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Thanks for the advice! I had to end up changing out the aquastat. Expensive weekend.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements