Adding a wall heat to existing radiant heat floor system
cseec
Member Posts: 1
I have a 5 zone radiant heat system installed 2 years ago. 4 zones are under the floor ,1 zone is baseboards. I'm adding 45 sq. ft. to a bedroom. The addition will be on concrete. Can I add a baseboard heater to the underfloor system?
0
Comments
-
You can... but will it heat much? If you are planning to tie into the radiant floor loop, you will need to know what temperature that floor loop runs at. Usually radiant floors run at much lower temperatures than are needed to make a baseboard heater put out much of any heat.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
That baseboard will need to have its own loop and pump (or zone valve running off of the boiler pump) connected to the high-temperature portion of the boiler piping. I assume the existing Baseboard zone is already operating from the high-temperature portion of the boiler piping. It should not be any real problem to design that. It can even operate via the same thermostat that operates that low-temperature floor zone. You may need a relay or get creative with the control wiring, but it's doable.
Mr.EdEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements