Pumping away
Ryan1234
Member Posts: 2
Since the common piping on a primary secondary loop (the space in between the tees) is considered a point of no pressure change, then shouldn’t the primary loop circulator pump away from the common piping? Would it be like having a circulator in between two expansion tanks if it were in front of the tees pumping into the common piping ?
0
Comments
-
-
-
@Ryan1234
I think your confusing two issues
The expansion tank is the PONPC no matter where it is installed, no matter what kind of system it is installed on, nothing to do wit primary/secondary
The closely spaced tee make the primary loop and the secondary loop "hydrolically isolated" from each other. A pump on the primary moving water has no effect on the secondary loop and vise versa1 -