Quick question about shifting riser piping
Dooverdixon
Member Posts: 49
So I need to move 2 radiators that are first a d only rads on the 1.25" riser. The riser comes straight up and goes into a 90 degree valve connected to the radiator.
Due to some wall changes I need to move them about a foot.
I see having 2 options. Easy...and harder
1) swap the 1.25 valve for an elbow add in a foot of pipe and a new straight valve and be done. (Will this create issues with condensate having a foot long section of 1.25 horizontal?? (Obviously sloped a bit).
2) come off the runout (1.5" pipe) with a 90 degree elbow. Add my 1 foot extension perpendicular to existing runout in 1.5". Then reducing elbow to 1.25 riser and into 90 valve.
Option 2 sucks because the pipe is old a d who knows what's going to happen. But I dont want to do it twice and I don't want to introduce a ton of gurgles and hisses into this system.
I guess a 3rd option would be using a reducing elbow and reducer to valve above the existing riser...this sounds ugly though.
Due to some wall changes I need to move them about a foot.
I see having 2 options. Easy...and harder
1) swap the 1.25 valve for an elbow add in a foot of pipe and a new straight valve and be done. (Will this create issues with condensate having a foot long section of 1.25 horizontal?? (Obviously sloped a bit).
2) come off the runout (1.5" pipe) with a 90 degree elbow. Add my 1 foot extension perpendicular to existing runout in 1.5". Then reducing elbow to 1.25 riser and into 90 valve.
Option 2 sucks because the pipe is old a d who knows what's going to happen. But I dont want to do it twice and I don't want to introduce a ton of gurgles and hisses into this system.
I guess a 3rd option would be using a reducing elbow and reducer to valve above the existing riser...this sounds ugly though.
0
Comments
-
There's a joker in the first option, too (though either option will probably work OK). The joker is that new straight valve. That will also require a new spud out of the radiator... and I'd much rather be fussing with old pipe than trying to get a spud out of a radiator. So if it were mine to do, I'd pick number 2.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I would pick #2 as well. But if the branch of the tee is 1 1/2" keep it 1 1/2" up to the valve. Either use a 1 1/4 x 1 1/2 reducing coupling with a short nipple under the valve or use a 1 1/4 x 1 1/2 90 in the riser just before it goes through the floor0
-
@Jamie Hall
I was planning on replacing the spud anyway because the current valve stopped closing and is pretty haggard. Is there any tips for this job lol. And does this change your recommendation. Hah???
@EBEBRATT-Ed
Thank you! For what Its worth the way its currently piped is 1.5 run out to 90 elbow reduce to 1.25 riser to valve. It prob not worth converting to 1.5 on the riser eh?0 -
You need to know the EDR of the radiators to know what the pipe can handle, right?0
-
If It's been hooked up with 1 1/4 with no issues you will be fine.
As far as removing the stub you have a few choices. My first choice is to cut the union nut off so you can get a good bite on it with a pipe wrench. Jamb something inside the spud (smaller pipe nipple etc) to keep the spud from collapsing.
They make spud wrenches that go inside the spud and grab on to the two little tangs inside the spud nipple but they sometimes break off.
I have also used a piece of steel square stock and using a grinder on the steel shape it to fit inside the spud and lock on to the tangs0 -
Why do you want to close the valve to the rad?—NBC0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements