tenant elbow rust
rabbitsfoot
Member Posts: 18
I'm a tenant. I saw this go off the other day at 30psi . The man who came to fix it said it was the compression tank...I think he drained it or filled it with air...said he didn't have replacement prv and needed to get one...said the system was put in about 3 1/2 years ago. I think it looks unsafe though this the first radiator furnace I've seen close up. How old can that valve be? Very new rust streak? I'm not going to get any closer than my camera . In the comments section of a you tube video by someone named Steven Lavimoniere ("Boiler Leaking Water Out Relief Valve"), a Michael Geary mentions his Weil McLain's deteriorating prv elbow and his concerns relating to possible boiler corrosion nearby-no one in those comments answered him though. I wondered if anybody here could. So the compression tank was fixed, I guess, and since the valve was also beading/sweating water out at the threads, it must have been tightened because it's been dry since the fix 30 days ago. worried though...Just saw the underside of the blower in this picture-and the little rust spot...that valve...
0
Comments
-
no picture...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
From here without any pics it sounds like the relief valve did its job and the issue was the Compression tenk. (were talking about a tank mounted on the ceiling)
As far as the relief valve its his decision if it can be pulled and reinstalled at the time he was there or if a replacement is in fact needed.0 -
0 -
pictures!0
-
Thanks. one or two a bit further back would be helpful too.0
-
That elbow may only be 3 or 4 years old. It is as old as the boiler. The boiler comes with it already installed in most cases. There are many, many years of life left in that fitting as long as the relief valve does not leak on it anymore. There should be a "safety tube" attached to the outlet of the relief valve to direct any discharge to a safe location near the floor. This will keep water from getting on the elbow causing more rust. A little elbow grease with a wire brush and the elbow will look like new. (one of the common uses for "Elbow Grease")
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
It looks like the drop pipe for the relief valve is laying on the floor. (picture with switch and pump).
Maybe was not screwed in and the valve dribbled for a long time rusting the elbow.0 -
0 -
Shouldn’t that be a P T relief?0
-
That automatic air vent on the cast iron fitting above the right side of the boiler(air scoop) is not correct if the system has a conventional compression tank type expansion tank. The system should have an air fitting that moves any air in the system back to the tank and no automatic vents. That automatic vent will cause the expansion tank to become waterlogged again.0
-
to mattmia: you mean this thing?0
-
-
How long might it take for all the air to migrate out of the tank, or for the tank to become waterlogged, if there's any difference?0
-
I have wondered about a T&P on water boilers, but have never seen one with the right parameters. Needs to be 30PSI for the pressure part and what temp?-- 200-210 degrees.
There have been some boiler installed T&P shown on the wall here, they were water heater tank rated. 125-150 PSI and 210 degrees.
Unknowing home owner changed his dripper, really fixed it well as it never opened again.
I guess we just have to rely upon electro mechanical high temp limit switches for the over temp protection.0 -
rabbitsfoot; I service a system that has an 80 gal compression tank.
It had an auto air vent on the piping, the air was being lost in the tank in about one season. Learned about the system more and removed the air vent.
Then air would last about 2 seasons.
Then learned the the convenient sight glass would loose air on the top fitting, then repacked that valve.....the air has been good for at least 4 years now.
Again can be viewed by the non leaking sight glass.
You can disable that vent by tightening the Schrader cap down tight.1 -
to JUGHNE : the system here has 11 big old radiators on two floors (none in attic). The tank is a 45gal "Jacuzz". Is "80 gallons" bigger for a larger system?0
-
-
are these old tanks usually being replaced with the bladder tanks by preference?0
-
Yes, most often they are replaced with bladder type expansion tank.
Usually a better air venter in installed at that time.
But the bladder tank would have to be changed in less than 10 years because of being water logged.
Your existing tank is probably 50-60 years old.
Also in your case the next size of tank up would be needed because of water volume.
For being the tenant you have quite an interest in all this.
Do you pay your own heating bill directly to the gas Co.?0 -
No. I just pay an all-inclusive flat rate. Nice house, nice neighborhood, nice guests. It's just the looks of that scaling elbow close to the boiler and what looks like a safety tube just below it that got me started. The threads look okay so I guess it wasn't blown off...but since I first moved in I did bleed the radiators with a key from the first floor up-shortly after another tenant bled them for the year, thinking it would get the last little bit of air out and make things warmer. after I later saw the valve spew I shut off the boiler switch seen on the picture. The guy who works on this didn't really like those last two things. Really, I'd rather not touch it.0
-
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements