Do mixing black pipe and galvanized piping cause pinhole leaks?
Dairon421
Member Posts: 80
Been doing boiler pipe repairs and majority of the leaks has galvanized mixed with black pipe. If this the reason can you explain to me why? If not what else could cause pinhole leaks in boiler piping.
0
Comments
-
It can, and probably will. Galvanized pipe is steel with a zinc coating, more or less well applied, and black iron is just that. Black iron. Steel rusts, and the galvanizing tries to protect it from that by being eaten away itself. I'd almost be surprised if you didn't get leaks at threaded joints where the two join. For that matter, I've noted that galvanized often just develops leaks on it own.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Jamie Hall said:It can, and probably will. Galvanized pipe is steel with a zinc coating, more or less well applied, and black iron is just that. Black iron. Steel rusts, and the galvanizing tries to protect it from that by being eaten away itself. I'd almost be surprised if you didn't get leaks at threaded joints where the two join. For that matter, I've noted that galvanized often just develops leaks on it own.
As far as I'm aware modern "black iron" is steel pipe with a protective coating and galvanized pipe is the same exact pipe but galvanized.
Even if one were actual iron I don't see why galvanized pipe would have an issue with that. Its not like mixing brass and aluminum or copper and steel. They're very similar.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Steam or Hot Water?
Cutting threads on a galvanized pipe compromises the galvanizing in the threaded area. So bare steel gets threaded into galv fittings all the time.
The mixing of galv and black that you see could be previous owners replacing the worst of the worse. I suspect the root cause of your pinholes is age and water quality, not mixing G and B.
How often is make up water added to your system?0 -
It will be a steel to steel connection, so no issue there. Steamers like a bit of alkalinity, so if you raise ph or add a conditioner, that too will protect the pipings insides.
Check the water ph after it runs a few days, adjust as per the boiler manufacturers recommendations.
Some info from the Rhomar manualBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements