Banging!!!!

Hello. I have recently removed a radiator in my attic and removed and recessed the steam pipe on my first floor. Boiler is in the basement. Since this project the banging that we get when the steam comes on can wake the dead. My neighbor hears it in her house!
im not a professional. Just trying to help sleuth it out because no one has been able to help us so far.
Any ideas?
im not a professional. Just trying to help sleuth it out because no one has been able to help us so far.
Any ideas?
0
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 567 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.2K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
EcoSteam ES-20 Advanced Boiler Control
Boiler pictures updated 2/21/15
https://www.facebook.com/media/set/?set=a.10202744301871904.1073741828.1330391881&type=1&l=c34ad6ee78
Would like some clarifications...
Q1) is this a single pipe steam system?
Q2) is the steam pipe going to the attic still in place, and shut from the valve after you removed it from the attic? what did you do with the pipe going to the attic?
Q3) Is the banging nose com from the attic steam pipe (assuming that pipe is still there)? or is the banging come from the first floor? or the basement pipes?
Q4) Did you install the attic radiator on the first floor?
Q5) What was the reason you decided to remove the radiator from the attic?
thanks and best!
LS123
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Removal of the rad let some piping in the basement (or somewhere) dip producing the sag full of water that the steam hits creating hammer.
I believe some angle may have changed somewhere but how can I possibly know where?
Can you see your piping in the basement?
1) Third floor pipe should be air tight that would prevent any steam going in to that pipe and water to build up some place. Once you make sure that pipe is sealed and air tight you know there is no steam going in to that pipe. Unless during the removal of the radiator on the third floor caused something cause air leak from first floor to second floor.
Q) I am not sure if you have isolated where the bang coming from. A) attic
once you make sure third floor pipe is fully sealed, no air leaks, that will most likely eliminate that pipe, assuming you do not hear the banging coming from the attic.
2) Make sure that the steam pipe on the first floor radiator in a slope... assuming single pipe steam. Also make sure that first floor radiator valves are fully open, and all radiators have a slope toward the supply pipe (assuming again single pipe system)
3) if you did make any changes to the pipe in the basement let us know what you did.
you can also do a process of elimination by doing below...
you can also do test by making sure that both third floor pipe completely air sealed tight and first floor radiator completely shut, and running the boiler for a while to see if you get banging noise (if it come from the basement)
secondly you can completely shutting the first floor radiator to see if the noise come from some pipe in the attic.
best.
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
I will try to go step by step.
Q1- I don’t know
Q2- all pipes still basically in place
Q3-banging coming along whole lane attic to basement.
Q4- no the attic radiator AND first floor radiators were eliminated
Q5- removed radiator in attic to create space for a walk in shower. It’s sealed into the tiled floor of the shower.
no changes in basement at all. And there is no more radiator on first floor either. Took it out and what was exposed vertical pipe got pushed back into the wall.
Thanks
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
You could pull up those risers and clamp them with any form of wood or C clamp just to see if it changes anything.
Is the copper pipe the steam pipe? (steam pipes should always be black)
Copper will tend to condense a lot more steam than black pipe so that could add to a banging issue.
Was it insulated prior to burying it in the wall?
It appears all those pipes are level where they run under the floor, that should never be, can you confirm?
If that pipe is the source of the banging, and you indeed aren't using it to feed any radiation, I would start by disconnecting it at the main and see what you get. If you still have banging at least you have eliminated one possibility.
EcoSteam ES-20 Advanced Boiler Control
Boiler pictures updated 2/21/15
https://www.facebook.com/media/set/?set=a.10202744301871904.1073741828.1330391881&type=1&l=c34ad6ee78
I will try to go step by step.
Doesn’t the pipe that’s going upstairs also go to radiators on the second floor before it reaches the attic? So would I be able to close that off?
Right above this bathroom is second floor bathroom eith a radiator. Maybe if I close this pipe completely and add electric heater to second floor bathroom I can eliminate the whole line. Is that a possibility?
If you didn't have banging before, and now do, something they did is making it bang. I only suggest disconnecting, because what it looks like in the pictures is the only way to fix it is to get to the pipe under the floor and redo it. That doesn't seem feasible based on what you have shown in the pictures, but I could be wrong on that.
To be clear all steam carrying pipes need to have slope, they need to slope so that the condensed steam (water) can easily and freely travel back to the boiler. It appears as thought the pipes that are now under your floor were put in level, this can cause banging, and would be my first guess as to the cause of yours. That and the copper isn't doing you any favors either. Copper will condense like crazy which can accentuate the problem. Again, if it wasn't insulated, which I'm guessing it wasn't, or you don't know.
If you ever have work done on your steam system again I strongly suggest you find someone that knows what they are doing. Where are you located as we may know some good contractors in your area?
EcoSteam ES-20 Advanced Boiler Control
Boiler pictures updated 2/21/15
https://www.facebook.com/media/set/?set=a.10202744301871904.1073741828.1330391881&type=1&l=c34ad6ee78
A couple of other thoughts. A vertical pipe can't bang. However, a horizontal pipe below one can bang, particularly if there is a radiator somewhere up above.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
the question is where to begin to rectify. I am in Brooklyn 11230
https://heatinghelp.com/find-a-contractor/
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
how could I even begin to guess where it’s poorly sloped?
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Steam Heat Enthusiast
-- In Learning Mode --
" Trust But Verify " Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Thank you all. Contractor has to open ceiling in basement anyway to fix some Sheetrock. When it will be open I’ll be able to see connections from downstairs looking up.
if I can see the line is just for the bathrooms I think I’ll opt to cap it.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch