pressuretrol question. is mine okay?

tumbztumbz Member Posts: 72
edited January 10 in Strictly Steam


is there a way to calibrate a pressuretrol? im trying to set mine to .5 cut in, and about 1 to cut out, but its weird because when i do that, the boiler doesnt run when it calls for heat the next cycle.

i would have to come back and turn the knob until the cutout reaches to about 2 before the system to fire up again.

does the CUT OUT mean the pressure at which the boiler is running at? I installed a new 1-5 gauge and when its steaming, the pressure is about 1 - 1.5. Im having banging in my main pipes, so i figure the lower the pressure, the better.

is this because of a cheap pressuretrol? i attached a picture of mine. It works properly, its just that when i set the cut out to 1, it wont turn on until i up it to 2......

can you guys suggest a better one?

Comments

  • Jamie HallJamie Hall Member Posts: 14,715
    In that pressure range, the Honeywell 0 to 4 psi vapourstat is far more precise (repeatable) and usually more accurate -- and is not that hard to calibrate.

    It is very likely that the one you have simply will not reset reliably below the pressures you are working with.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • tumbztumbz Member Posts: 72

    In that pressure range, the Honeywell 0 to 4 psi vapourstat is far more precise (repeatable) and usually more accurate -- and is not that hard to calibrate.

    It is very likely that the one you have simply will not reset reliably below the pressures you are working with.

    due to my hammering and my old pressuretrol not being able to set the steam at a lower pressure, i think ill buy a vaporstat.

    is this model number okay?

    Honeywell-L408J1009-Vaporstat-Controller-Steam-0-to-16-oz to work with my boiler.
  • Jamie HallJamie Hall Member Posts: 14,715
    Is this one pipe or regular two pipe? If so, I think the L408J1017 might be more suitable, as it can be set from 0 to 4 psi. The L408J1009 has a maximum setting of 16 ounces, and is more suited to vapour steam systems.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • tumbztumbz Member Posts: 72

    Is this one pipe or regular two pipe? If so, I think the L408J1017 might be more suitable, as it can be set from 0 to 4 psi. The L408J1009 has a maximum setting of 16 ounces, and is more suited to vapour steam systems.

    i have a 1 pipe steam system. so i should buy the L408J1017 ?
  • Jamie HallJamie Hall Member Posts: 14,715
    yes
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch

Leave a Comment

BoldItalicStrikethroughOrdered listUnordered list
Emoji
Image
Align leftAlign centerAlign rightToggle HTML viewToggle full pageToggle lights
Drop image/file

Welcome

It looks like you're new here. If you want to get involved, click one of these buttons!