Rod KotigaRod Kotiga Member Posts: 68
Over the years I’ve seen many posts about Maximum loop lengths of different pex sizes but never a minimum.
For example, What if you have a staple up system with plates of course but your thinking about just running a supply and return main to pick up each joist space run separately. I know some might think that’s a lot of tees but plastic tees aren’t that expensive and as long as all the loop lengths are equal what’s the downside? 
Rod K

Comments

  • Mosherd1Mosherd1 Member Posts: 1
    I’m thinking of doing the same in my crawl space. I know I don’t have the room to work with 250 feet of pex runs under there, my nose touches the bottom of the floor joists in parts while I’m laying on my back, but if I can do a full loop per joist space and do a reverse return I should think it would work as I’m just using it for floor warming not my primary heat source.
  • ZmanZman Member Posts: 6,312
    If you use an uncoiler and pull the loops through the bays one at a time, 250' is not difficult to work with. I am not sure why you would want to add all those connections...
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • EdTheHeaterManEdTheHeaterMan Member Posts: 1,557
    edited January 8
    You are correct, That will work just fine.

    I have one question. How are you going to purge the air from each individual loop? Are you climbing under the floor in the crawlspace and have a purge valve on each joist bay?

    That air will be purged based on the principles of physics. The water will take the path of least resistance. Once one or two of the loops are air-free, the rest of the loops will have more resistance and resist purging the air.

    When I did my last home, I put the manifolds in the wall cavity so I would not need to go in the crawl space ever to purge the loops.
    Edward Young
    Retired HVAC Contractor from So. Jersey Shore.
    Cleaned & services first oil heating system at age 16
    Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air

    If you make an expensive repair and the same problem happens, What will you check next?
    Zman
  • Solid_Fuel_ManSolid_Fuel_Man Member Posts: 2,239
    I dont think there is a minimum. You could even use smaller then 1/2" if you can get the plates. May be no advantage other than being the most workable. 

    I've done several radiant jobs with nothing more than a ball valve per loop and a bunch of reducing Tee's. Purges fine, and simple reverse return. That way you just need one purge station, do 3 or 4 loops at a time. Never had any air issues. 

    Pump toward the loops (after the mixing device) and all works wonderfully. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Solid_Fuel_ManSolid_Fuel_Man Member Posts: 2,239
    This is a small basement radiant job, needed very little heat. Customer couldnt be happier.  
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    BillyO
  • Dave H_2Dave H_2 Member Posts: 412
    Think of it this way, the main reason you are running a radiant floor system with pex is because of it's flexibility and lack of connections. Every connection you make is a threat leakpoint.
    If it's the flexibility you are looking for, consider running 3/8" instead, night and day difference

    Dave H
    Dave H
  • Jamie HallJamie Hall Member Posts: 14,797
    @EdTheHeaterMan has a good point about purging. It will be almost impossible with multiple short loops. However, there is another problem even more fundamental: the resistance to flow in a loop is inversely proportional to effective loop length. The effective loop length is the length of the pipe, true -- plus all the miscellaneous losses along the way from bends, Ts, elbows, kinks, etc. etc. As the length of pipe gets shorter, those miscellaneous losses get greater; on very short loops they will become dominant. As has been noted, water is lazy. I those multiple loops are piped in parallel, some will get far more low than others, and the heating across the floor will become patchy.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • hot_rodhot_rod Member Posts: 14,384
    Yes it would work fine with reverse return, I too would go with 3./8 purge with city water pressure and you will get an adequate purge.
    A Dahl ball valve with pex adapter would be nice on each loop for somem adjustability and purge ease.

    I have seen a few jobs where copper headers ran the length of the crawlspace with short loops. The pex connections properly done should not be a problem, most pex plumbing systems in homes have hundreds of pex connections, under much higher pressure.

    https://www.pmmag.com/articles/88420-extended-thinking-br-john-siegenthaler-pe
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
    Solid_Fuel_Man
  • TAGTAG Member Posts: 394
    I just did the great room of my current project -- 1000sf room --- using extruded plates and 3/8 pex. It went very well and the 3/8 pex is so much easier to work with. The loops are 160' -- 11 loops to the manifold. Remote manifold piped with 1.25 copper.

    We used a bluefin manifold -- you can't use the 3/8 bluefin fittings w/ viega brand pipe .... they leak. I got other fitting and it working great ... we power flushed it
  • EdTheHeaterManEdTheHeaterMan Member Posts: 1,557
    All good stuff to think about. Aren't you glad you posted here so you can get this valuable info @Rod Kotiga?
    Edward Young
    Retired HVAC Contractor from So. Jersey Shore.
    Cleaned & services first oil heating system at age 16
    Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air

    If you make an expensive repair and the same problem happens, What will you check next?
    Rod Kotiga
  • TAGTAG Member Posts: 394
    edited January 9
    BTW -- I had never used 3/8 pex with the plates prior to getting advise and recommendation here on the forum .... had used it for a house where we did wet bed tile and did not want to have the floor too thick --- but not retrofit plates.



  • EdTheHeaterManEdTheHeaterMan Member Posts: 1,557
    edited January 9
    Rethinking my radiant system. I believe I used 3/8" PEX with aluminum plates. Me and a helper. We made 200 to 250 ft loops and fed 4 to 5 joist bays at a time... in a crawl space... It was not that difficult once we got a system going. 1400 Sq Ft of hardwood floor above us and we got it done in 2 days.

    A year later I was able to have another of my technicians do the manifold piping and install the boiler. 3 years prior we installed an addition that was a Slab on grade. 2" foam board on the ground and the perimeter before the pour with 6 loops of 1/2" PEX left idol in the crawlspace. (I left a 20 PSI pressure on the tubing for the 3 years and it held the whole time.) Once the staple up was completed I had Spray Foam insulation applied to all the floor joist spaces.

    Loved that heat! Sorry I had to leave it.

    Oh well, it is what it is!

    Yours truly,
    Mr.Ed

    P.S. Damn, My feet are cold!
    Edward Young
    Retired HVAC Contractor from So. Jersey Shore.
    Cleaned & services first oil heating system at age 16
    Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air

    If you make an expensive repair and the same problem happens, What will you check next?
  • hot_rodhot_rod Member Posts: 14,384
    Rethinking my radiant system. I believe I used 3/8" PEX with aluminum plates. Me and a helper. We made 200 to 250 ft loops and fed 4 to 5 joist bays at a time... in a crawl space... It was not that difficult once we got a system going. 1400 Sq Ft of hardwood floor above us and we got it done in 2 days. A year later I was able to have another of my technicians do the manifold piping and install the boiler. 3 years prior we installed an addition that was a Slab on grade. 2" foam board on the ground and the perimeter before the pour with 6 loops of 1/2" PEX left idol in the crawlspace. (I left a 20 PSI pressure on the tubing for the 3 years and it held the whole time.) Once the staple up was completed I had Spray Foam insulation applied to all the floor joist spaces. Loved that heat! Sorry I had to leave it. Oh well, it is what it is! Yours truly, Mr.Ed P.S. Damn, My feet are cold!
    It’s hard to live with any other heat system once you experience properly installed and controlled radiant 
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
    EdTheHeaterManSolid_Fuel_ManBillyO
  • Solid_Fuel_ManSolid_Fuel_Man Member Posts: 2,239
    I built my house as a heated slab on grade. Here in the far northeast everyone has a full basement. I have hard ledge everywhere, and didnt want to bla$t. 

    I would absolutely do it again, just takes planning before the pour to have all mechanical stubs in the correct locations. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    motoguy128
  • motoguy128motoguy128 Member Posts: 329

    I built my house as a heated slab on grade. Here in the far northeast everyone has a full basement. I have hard ledge everywhere, and didnt want to bla$t. 

    I would absolutely do it again, just takes planning before the pour to have all mechanical stubs in the correct locations. 

    2/3rds of the new construction in my mostly rural area is slab on grade even though most typical homes have basements (SE Iowa, 5F design). I really like the concept. Downside is you lose storage space without a basement so you need a good garage attic area with pull down stairs. Most customers also build vaults as well as a storm shelter (tornado country) and for their guns, of course.
  • hot_rodhot_rod Member Posts: 14,384

    I built my house as a heated slab on grade. Here in the far northeast everyone has a full basement. I have hard ledge everywhere, and didnt want to bla$t. 

    I would absolutely do it again, just takes planning before the pour to have all mechanical stubs in the correct locations. 

    2/3rds of the new construction in my mostly rural area is slab on grade even though most typical homes have basements (SE Iowa, 5F design). I really like the concept. Downside is you lose storage space without a basement so you need a good garage attic area with pull down stairs. Most customers also build vaults as well as a storm shelter (tornado country) and for their guns, of course.
    Scaredy (sp) holes is what we call those dual purpose rooms here in Missouri. A builder friend of mine found an old bank vault door for his concrete room.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
    Solid_Fuel_Man
  • YoungplumberYoungplumber Member Posts: 194
    @motoguy128 SE iowa huh? Burlington is where I call home.

    Also not trying to pick a fight but I thought design temp is - 3.
  • Rod KotigaRod Kotiga Member Posts: 68
    What hotrod said 👌
    Also I’ve done several staple ups doing the 250’ loop length thing.
    but sometimes there’s a lot of obstacles in a crawl space ( even one that’s 4’ deep) and as in some cases your fighting a little with the coil and that’s what’ll make you think about a long supply and return main and be done with it.
    Being a plumber as well we all put a ton of pex fittings in the crawl and in the wall at higher pressures than radiant so more connections is not a worry as it’s all tested anyway.