Honeywell RA832A thermostat relay loud buzzing
speedbird
Member Posts: 23
Hi everyone, I have a hot water line (off our steam boiler) that feeds 2 toekick heaters in the kitchen. Not a huge fan of the design for many reasons, but it's how previous owners did it. Needless to say everything works well.
That said, the RA832A relay makes a terrible buzzing sound when that kitchen thermostat calls for heat, and runs the circ pump. It's a 2004 model so maybe it's just time to replace it? I have a shop down in the basement and it drives me insane.
An electrician told me it just put a piece of electrical tape over the particular piece that vibrates next to the coil. That seems to work but afraid it's interfering with operation, and it'll fall off eventually.
0
Comments
-
You need to check if you are getting 24+ volts to the coil. If you are and it still buzzes, replace the RA832. If not, find out where the voltage drop it. Transformer not making 24 volts (unlikely) long undersized thermostat wire...maybe....or poor contacts in the thermostat (R&W).
At least try jumping out the TT on the control and see if it still buzzes. Also, make sure you have 120 volts to the control, not something less.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Honeywell is aware of this problem and addresses it in its instructions.
here is the full instruction sheet: https://s3.amazonaws.com/s3.supplyhouse.com/product_files/RA832A1066-Install.pdf
The noise is a normal byproduct of alternating current (AC) that sometimes makes a mild humming noise at 60 cycles per second (Hurtz). I will tell my customers that it's humming is because they forgot the words but, if the buzzing is too loud you can try adding felt or tape or any other vibration dampener that works. As long as it does not interfere with the operation of the mechanical parts of the relay.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Able to confirm I have 120v coming into the control but cant seem to get a reading across the TT terminals. Reading 0v. I think I'll just tape it down for now and order a new one. I'll add those rubber washers this time around.0
-
I the thermostat is calling for heat, you should get 0 volts across the T-T terminals. That is correct. When the thermostat is off, then you should read at least 24 volts.
If you can access the coil terminals of the relay, check the voltage with the thermostat calling. If it is less than 24 volts, there's your problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Good call. 24v across TT. I know it was mentioned earlier too, any idea how I'd check voltage to the actual coil?0
-
The truth is you will read around 15 volts across T T as you are including the resistance of the coil when you go across T T the remainder of the voltage is being dropped across the coil. If you read lower than 15 then the coil is dropping too much and the relay needs replaced.
0 -
Ok I'm reading 24v across TT when it's not calling for heat.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements