Unpopular opinion - Riser vents > main vents?

Options
jlbk
jlbk Member Posts: 14
I have one 4 story building with no main vents but has 2 risers, front and back, supplying all the heat, and they are tapped and vented. The riser gets hot in 5 mins from the header, and the radiators are hot in another 5-7 minutes. Compared to other properties that I installed a big mouth on, the main gets hot in 2-3 minutes, but it takes another 10-15 minutes to reach the top floor.

The clear answer seems to be to vent these risers as well. This leads to my second question, can i avoid tapping the risers and just tee off the last radiator on the run with a 1/8 tee and add two gorton d? Can the last radiator on the line vent too fast?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,286
    Options
    In answer to your question on teeing off the last radiator on the run for a vent -- that works. And if that vent is before the radiator, while it may alter when the radiator starts to heat, it won't change the rate at which it heats once it starts.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,524
    Options
    @jlbk

    If I understand you system correctly you said you have two riser that carry all the heat. If this is true the top of the risers is basically the end of the main.

    The second part, if you mean adding more venting to the top radiator I would not do that the rad may overheat. Try it if you want but I would vent the radiator inlet and leave the radiator vent alone
  • jlbk
    jlbk Member Posts: 14
    Options
    Yea right the riser is the end of the main. So wouldn’t all risers technically be the end of the main then? Wouldn’t tapping vents on all risers be just as important if not more so than having a main vent?
  • New England SteamWorks
    Options
    Install a regular main vent at the top of the risers, not an 1/8” radiator vent. Do so by replacing the angle valves on the top radiators with a tees, then connect to the radiator with a straight valve. 
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • bburd
    bburd Member Posts: 913
    edited December 2020
    Options
    Steam flows through pipes due to pressure differential, not gravity.

    Bburd
    ethicalpaul
  • jlbk
    jlbk Member Posts: 14
    Options
    I agree installing a main vent on the riser or the valve is the proper way to do it, but can I take the easy way out by doing a 1/8 antler out of the radiator tapping? 
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited December 2020
    Options
    Hmmmmm
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    edited December 2020
    Options
    There is a lot of mixing of ideas in your paragraph, @betweentheframe. @bburd said it so plainly and correctly above.

    Steam in a riser pipe is not really like warm combustion gases in a chimney--the chimney is open at the top and bottom. But that's really beside the main point:

    The movement of steam in our pipes is vastly (might as well say completely) due to pressure differentials between the boiler which is producing steam (and increasing pressure) and all the pipes in the system. The pressure increase moves in waves until it (and the air in front of it) finds a way out. That is where the steam will go, whether it's up, down or sideways.

    Edit: PS:
    pressure exists because of gravity

    Atmospheric pressure does, but not all pressure does. An oxygen tank and supply line in space works with no gravity.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    Options
    jlbk said:

    I agree installing a main vent on the riser or the valve is the proper way to do it, but can I take the easy way out by doing a 1/8 antler out of the radiator tapping? 

    An easier way out that will keep your radiator heating at about the same rate as it does today would be to use a tapping on the same side as the supply pipe. Put a #D or #1 size (using MoM or Gorton sizing numbers) on that tapping, and put a nice slow #4 on the (normal) opposite side tapping. Many radiators have tappings on both sides with one of them plugged.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • Gsmith
    Gsmith Member Posts: 431
    Options
    Another factor not mentioned is the pipes and radiators condense the steam to water at 1\1700 the volume which creates a vacuum drawing the steam towards the cooler (than steam) radiators. Helps a lot with the distribution once the steam gets to the rads.
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited December 2020
    Options
    @betweentheframe. So you feel the difference in weight between steam and air is enough to push the air out of the vents at the speed it does?

    I calculated the pressure drop in my piping to each radiator and oddly enough it's roughly what the boiler runs at.

    I'm sorry but, if you have a single pipe system with air vents it's not running at 0 psig.  Either your gauge isn't sensitive enough and or its been pulled into a vacuum by a pigtail.


    Mine runs no lower than 0.009 psig which is the pressure drop to the furthest radiators.


    And no, I do not feel the weight of the steam is having an effect.   The steam condensing and creating a vacuum does though.  Even in my mains as the steam "inch worms" down the pipe.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    edited December 2020
    Options
    I don't want to hijack this poor thread any more, but there's a lot of wrong things here I'll address just this one more time, then if you want to discuss it more, start a new thread called something like "why steam goes where it goes" or something and I'll find it :)

    That’s a half truth:..If you remove all rads and have nothing but steam pipes coming out of the floor (or as when system is cool and valves are open) you will have a zero pressure system,


    No you won't. You'll have a greater pressure in the boiler, which then pushes the air toward the places with less pressure just like I described before. That could be up, down, or sideways


    but the steam will still move up and out of the pipes because it is lighter than the air.


    No. It will move out of the pipes because steam is being generated behind it, builds a small amount of pressure and starts pushing it. Up, down, or sideways.

    When the vents are all open when a boiler fires up there is no pressure, the steam displaces the air because it rises.


    No. The steam does make pressure (yes at first a very small amount, but more than enough to overcome any gravitational effect. And it pushes the air out of the pipes, up down, or sideways.


    It will not work wether it is up or down, because the steam is lighter than air, yet alone water, which is why you have to have the rads above the water line.


    It will absolutely work whether it's up or down. The reason rads are above the water line is so that the radiators don't fill with water.

    Air becomes more dense than steam above 324F and it becomes more complicated. But it is essentially true that hot air(steam is a gas) rises.


    In an open space, the less dense stuff rises. But in a closed system, it's pressure that rules the day. And you're right...it's also pressure that makes warm air rise in a room. But there's no pipe to guide it, so it just rises.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    Atmospheric vented steam systems are not closed systems. That is my point! Until all the vents close!
    That's good and all, but steam isn't going to climb past it self in a closed pipe full of steam. 

    You can have a single pipe system 99% full, but with all radiator vents still open and air vs steam weight isn't going to have an effect on that.


    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    Options

    And no offense but a thread about riser main vents and “main” vents is the appropriate thread to discuss where steam goes and why, and you can tell someone else where they can and can’t discuss the said topic. 

    I said I wouldn't respond more. (but now I have broken my word). You can keep posting wherever you like of course. But if you want to talk to me more on this topic it will have to be on a different thread from the poor poster who just asked a question about his vents :)
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • bburd
    bburd Member Posts: 913
    edited December 2020
    Options
    @betweentheframe, you wrote:

     I’m just an idiot with a boiler, but if it wasn’t this say you’d put the boiler in the attic”

    Some tall buildings with steam heat do put the boilers in the attic, and use pumped condensate return. It works fine.

    This makes rentable square footage on each floor of the building available that would otherwise be dedicated to a chimney shaft.

    Bburd
    ethicalpaulbetweentheframe
  • jlbk
    jlbk Member Posts: 14
    Options
    Hah, I came to check on my thread after a day and I saw 14 new responses. So sad that none of it had to do with my question. 
    ethicalpaul
  • jlbk
    jlbk Member Posts: 14
    Options
    Ethicalpaul, how do I remove this plug? Just drill it and thread it? Or is there an easier way?
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    Options
    So you did see my reply in there 😅

    And you do have the vent port plugged on the pipe side, then?

    Some can be unscrewed, some must be drilled. Can you post a photo of it? 
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,524
    Options
    I am having a senior moment.

    Whats the steam system where they send the steam main off the boiler straight to the attic. Then the main circles the attic with tees with branches dropping off the main feeding down to the radiation?

    It was designed by a guy that worked for HB Smith. John "something" It's described in the LAOSH
  • bburd
    bburd Member Posts: 913
    Options
    I believe that main pipe from the boiler to the attic is called an “express riser”.

    Bburd