Radiator vents “breathing,” other oddities. Service plumber needs help!
Ambivalence_83
Member Posts: 11
I’m a service plumber in an area with lots of steam heat and I can’t figure out what’s going on in my own house.
House was oil with a cracked boiler *surprise!* I converted to gas. No idea if these issues were here previously.
1. One first floor rad stays quiet during heating, then suddenly releases a huge loud rush of air out of the vent.
2. One second floor rad vent “breathes” loudly. Blowing air, sucking air, and sometimes the huge hiss like above. Lasts a long time too.
During all this, checked the boiler and saw the gauge at 4psi.
The facts:
House built in 1922.
An addition was added with a piece of steam baseboard. Has a steam trap on it.
Properly sized brand new gas steam boiler (sized based on square feet of steam).
All brand new vari-vents on all rads.
Brand new Gorton #1 on the end of the main.
All rads have pitch toward the valve.
All valves fully open.
Supplies to rads have proper pitch.
Honeywell Pressuretrol set to .5psi with 1psi differential.
Pigtail is not clogged.
Return is not clogged.
I’ve tried throttling the gas to reduce the firing rate, but it did not change anything.
I’m stumped.
0
Comments
-
irst comment would be -- is that pressure reading from the code 30 psi gauge? If so, it's dubious. If it's from a low pressure gauge -- there's a problem with the pressuretrol. Pigtail clogged? But you say you checked that. Or something amiss with the pressuretrol?
Panting vents are almost always due to water pooled somewhere in a pipe. I know you've checked that all the pipes have proper pitch, but is that end to end, or every inch? An older house may have had sags developed in the pipes which can trap a pool -- which may not hammer, but may give that panting behaviour.
One note -- don't fiddle with the firing rate unless you have, and know how to use, the test instruments for draught, excess air, oxygen, carbon dioxide, and carbon monoxide.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I checked every bit of the line feeding the most troublesome of the radiators, which is the 2nd floor bedroom one.After more research, I’m beginning to think the 1” supply/return pipe (single pipe system) is too small for the size of this radiator, which is large for a room of its size.Based on other recommendations, I’m going to try a smaller vent to slow down the process and see if that helps.And adjusting the gas flow was just an experiment to see if it made any difference in the interest of narrowing down the possibilities.0
-
1"? One pipe steam? That is probably too small. The maximum EDR for a horizontal 1" pipe is 28.
If you don't have it, you really should have your own copy of "The Lost Art" (from this site) and make yourself into the local expert!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Most of my radiators are piped using 1" vertical runs that go down into 1 1/4 horizontal.
We need pictures of the piping around the boiler as well as the gauge glass clearly showing the water.
Bonus points for pictures of the radiators and vents.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
Why is that trap there?Retired and loving it.0
-
I’ll get photos tonight.And I’m not sure Dan. I didn’t alter any of the existing piping.Thanks all!0
-
If it's one-pipe steam and there's no boiler-feed pump that vent shouldn't be there. Check to see if the trap discharges into a wet return or the steam main.Retired and loving it.0
-
Another development is that there is a main vent at the end of the supply run. It was just hidden in a wall.I replaced it with a Gorton #1 and raised it up with a nip and coupling.It hasn’t made a huge difference in the problem radiators.The baseboard install looks sloppy and I’m betting it wasn’t done properly. The baseboard does have it’s own return line though.0
-
If you are sure you have adequate main vents, consider changing the radiator vents, which you said are vari-vents, and replacing them with slower vents or adjustable vents like vent-rite or Hoffman. The varivents are almost always too fast for radiators and can seriously unbalance the system0
-
I had panting, hissing, train whistle issues with one radiator myself. Hypothesis was the valve wasn't open all the way and was causing water + steam collision and pooling.
Had the valve replaced. No more issues0 -
Ok. Pictures of what’s going on.The radiator in question.The boiler (forgive the Pro Press, I’ll be replacing it with black pipe).
The supplies for the first floor rad (quiet, then huge rush of air, 1 1/4”), 1” black pipe going to 2nd floor rad that “pants” and the 3/4” copper return for the baseboard with steam trap.
Supply to baseboard is 1 1/4”0 -
The picture of the three pipes is the first floor rad, second floor rad, and the return for the baseboard.
The pipes are pitched properly. Both break the bubble all the way to the main.The main vent is in the wall at the end of the main (pic with all the model airplanes).0 -
Going to replace the vent and valve on the 2nd floor rad and see if that helps.0
-
In the airplane room, the main on the left looks pretty flat.
Does it slope down away from the boiler draining towards the section of the main on the right?
0 -
Why is the trap in that radiator?Retired and loving it.0
-
JUGHNE said:In the airplane room, the main on the left looks pretty flat. Does it slope down away from the boiler draining towards the section of the main on the right?0
-
DanHolohan said:Why is the trap in that radiator?Should it not be there?0
-
Don’t know. I didn’t put it there. It’s on the return line of a 10’ piece of 1 1/4” steam baseboard.Ambivalence_83 said:DanHolohan said:Why is the trap in that radiator?Should it not be there?
If it's on a return line, and if that return goes, in fact, to a return, you do need it -- unless the return at that location is wet. In which case, you don't. However, there must be a way for air to get out, too. What is it?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
And if this is one-pipe steam and the trap is connected to a pipe above the waterline, it’s connect to the steam main. That can’t work. The there’s steam on both sides of the trap.Retired and loving it.0
-
Jamie Hall said:
If it's on a return line, and if that return goes, in fact, to a return, you do need it -- unless the return at that location is wet. In which case, you don't. However, there must be a way for air to get out, too. What is it?DanHolohan said:Why is the trap in that radiator?Should it not be there?The baseboard isn’t the issue here though, as it does heat. It’s mildly noisy but not overly so.0 -
DanHolohan said:And if this is one-pipe steam and the trap is connected to a pipe above the waterline, it’s connect to the steam main. That can’t work. The there’s steam on both sides of the trap.Every radiator in the house is single pipe.The baseboard supply comes off the supply right above the boiler (picture 3, first tee after the new copper).
The baseboard runs along this wall over an unconditioned crawl space.
It returns back into the basement in 3/4” copper, into the trap (picture 1) and returns to the boiler return at the lowest point (picture 3, 3/4” copper line with bend in it. Far left).0
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 87 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 907 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.7K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements