Weil-McLAIN boiler ECO boiler control broken

Harold
Harold Member Posts: 249
I bought that boiler several years ago. A few days ago the controller (I believe it is the problem) decided it would only support the DHW. No changes; just broke. And the control panel also hung up on just the DHW - then turned into an unusable screen junk that had become useless. I have no idea what is going on. This will be the fourth time we have lost heat in the winter because of the multiple boilers. And it is already a week.

Having some issues over a bunch of years, I had bought a controller and display "just in case". Unfortunately, I bought the wrong controls. I initially thought I had bought an EVG boiler - wrong. So now it is broken and my carefully stashed away controller is actually for the EVG I thought I had, not the ECO. I did not setup this controller. And just for the sheer joy of it, the installation for the whole control system may be used for automatic configuration ONLY ONCE and then you have to go back and do it manually. And manual is a serious mess to do. That is not my field of expertise.

I have spent a lot of time on trying to figure out a way to use the EVG set. It was rather expensive. I am hoping there is a way to deal with this. Looking at all the pieces, there seems to be some possible approaches. I was in the process of figuring out how to do that. And I ran into a couple of barriers. The most inconvenient location is the changes to P2 and P4. For these two, the number of circulators has gone from 1 in P4 for the "boiler circulator" and P2 adds a third circulator so there are the same circulators to use. I believe I only will need 2 like they were using before. They also changed the socket connector in P4. I don't have anything to substitute for the connector identified as that Boiler circulator. If I do not use the circulator in P4 I could open up the case and wire around the new wire distribution.

Some wires change pins locations but use something in the same little set of pins.

If I can find a socket matching the long P4, I might be able to be cut a hole under the wire around the new ones and mount above. Soldering and sucking (don't be nasty) I am good at.

I look forward to an instant solution from the forum :p



Comments

  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    You need the correct control. 

    If it's a gen 1, then it would be

    model1176-120
    W-M replacement 381-330-018. 

    Did you try shorting terminals 1 and 2 on P15 to see if a call for heat happens? You may have a DHW stuck, so try disconnecting 4 and 5 on P11. 

    I've had these freeze up on the display, and unplugging and replugging the 4 wire connector to the display will sometimes unfreeze them. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    kcopp
  • Harold
    Harold Member Posts: 249
    Thanks. The original part number is a ECO 550-225-396_0916.
    The wrong one is Evergreen 550-225-406_0817

    I will put the original controller back in and try what you suggest. And if you have any further suggestions.

    The way it was behaving when it initially stopped working properly. The main control from the controller on the wall for all the control points and it said "no heat". While that was cycling off and on, the boiler kept short cycling for only the DHW. Never went to the other heat requirements.

    I will probably buy a replacement soon since I have not been real successful. It is more than a week and it is cold out here. It is not very comfortable.

    If someone out there has a like new controller and display for the ECO and like to get rid of I would be interested.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,380
    another reason why I don’t like Weil-McLain.  Proprietary expensive parts that don’t fit other models.   They don’t even fit the same models from one year to the next

    rarely did I have the correct part on the truck for those crazy controls they use.   

    I know this is no help to you.  I just hope someone is able to read this and select another brand boiler. Maybe this post will pick up Velocity and that would be a CROWNing achievement 

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    WMno57STEVEusaPA
  • Harold
    Harold Member Posts: 249
    I am getting nowhere; but quickly.

    I put back the original controller. Still garbage. The display device is largely unreadable. So I still do not have a solution. I have no idea how to deal with this situation. It looks rather like really old Sanskrit. I think I could make the newer version if I cut up the socket they used in one location. I could try snipping out that one connector and solder everything.

    Is there anyone out there that knows enough about the controller and knows if the removing the odd socket would be the last thing I needed to do. It is P4 and got reconfigured. They went to a new connector design.

    I am afraid I am going to have to buy both a new controller and the display. It is quite expensive. I thought I did a good thing moving from an earlier boiler that had problems. I really don't want to buy yet another boiler. But we are getting quite cold in the house. And my wife is rather fragile.

    Ideas appreciated.
  • flat_twin
    flat_twin Member Posts: 354
    Harold said:

    Thanks. The original part number is a ECO 550-225-396_0916.
    The wrong one is Evergreen 550-225-406_0817

    .

    I'm confused by what you say is the original part number. The one solid fuel man provided is the correct number for a series one Eco boiler. I checked my installation manual and I don't see any Eco part numbers that begin with 550.


    Solid_Fuel_Man
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    If the display is garbage, it's driver is toast. How much the other chips on the display or in the controller are functional is anyone's guess. Just changing plugs or wiring is not going to change that.

    I have to admit that if I could get access to the burner controls directly I'd go old school -- but on that boiler (or, for that matter, any of the new advanced boilers) you can't.

    In my humble opinion, you -- or your contractor -- will need to source the correct display and control module for that specific model boiler, and install them.

    And, while you are at it, provide a good computer grade surge protector on the 120 VAC input power line.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    kcopp
  • Harold
    Harold Member Posts: 249
    Those two numbers are the part numbers for the ECO series 2 110 that is "in service" and the other one is for the incorrect
    spare controller which is probably not going to be used.

    The failure was sudden. It started running the DHW for short times, then doing it again. Essentially short period (maybe a few minutes) forever. No heat for the rest of the installation.

    At the beginning of strange behaviour, the house heating control system indicated NO HEAT.

    I do have a high grade surge protector. It is saying with the little green lights that is OK. We did nave a power outage about a week before this happened.

    I thought I could get somewhere with the spare controller - but one changed socket stopped be. I am not sure where I could get something to jerryrig. It should work if I could just do new wiring by cutting up something with the spare. The connections required are soldered to the mother board. Simplest would be to make up plug and put it in where it needs to be. But I do not recognize the socket.

    I have been sitting here trying to figure what service vendor to choose. Selecting one can be tricky. I am in the area of Burlington WA. There are a bunch; but getting one that understands the boiler could get a bit iffy.

    If I had the two plugs to put in the sockets on the board, there is a high probability it will work. I do not see any other booby trap that I can not deal with.

    I have screwed around for a week now. It is pretty cold in here. Wife is sick.

    The plug on the board is 1 1/4" long, and 1/4" wide. There are 5 male pins in the holes of the board socket. The holes on each end of the socket have a flat side on one side. The flat sides would be to key the two plugs. The one end has two pins used, and the other end has 3 pins used. So I would need individual sockets to fit over the 2 sets of pins.

    Individual wired sockets fitting over the pins on the board could work. All of the pins are power suppliers.

    If anyone knows of a matching plug (or creative ideas) - please let me know. It is not being fun.
  • flat_twin
    flat_twin Member Posts: 354
    Not sure where you got those numbers but they still don't agree with the Installation Manual

    Eco Series 2 Manual pages 124-125...

    Control module and housing 381-330-029
    Display board and housing 381-330-030

    https://www.weil-mclain.com/sites/default/files/field-file/Weil-McLain_ECOSeries2-BoilerManual_0119-web.pdf


    Is your boiler an Eco Tec combi boiler with tankless DHW?
    Solid_Fuel_Man
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I've seen the controllers on Ebay for around $200 or less. 

    I've scanned Ebay for you, but no dice right now. If I had a spare I'd send it to you to try. 

    I do know the boiler will run without the display connected. So if the display were fired the boiler would still function. But I'd bet it's the controller. 

    What does your plug look like?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,380
    edited December 2020
    You may need to wait until Monday and call WM tech support. +1 (800) 368-2492

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Harold
    Harold Member Posts: 249
    WM does not talk to civilians as far as I can tell.

    The set of pins are in the upper right corner of the EVG controller. The plug on the EVG board is 1 1/4" long, and 1/4" wide. There are 5 male pins in the holes of the board socket. The holes on each end of the socket have a flat side on one side. The flat sides would be to key the two plugs. The one end has two pins used, and the other end has 3 pins used. So I would need individual sockets to fit over the 2 sets of pins.

    Part numbers: They are what is printed on the manual pages. One part number is the normal controller for an ECO boiler. Which is my installed boiler. The other controller I tried to use is the controller for an EVG. I am reasonably convinced that the EVG controller would work if I chopped up that one set of pins.

    flat_twin - I do not understand what your point is.

  • Harold
    Harold Member Posts: 249
    I will try the link to support.
  • flat_twin
    flat_twin Member Posts: 354
    edited December 2020
    Harold, You have a Series 2 Eco boiler. I finally figured out the numbers you're providing are for the diagram in the manual not the actual part number. When WM provides certain diagrams like the wiring scheme for their control modules, they assign a part number to the diagram itself. I found this for the Evergreen and the Eco Series 2. Notice on every page in the manual 550-142-190/0119 is given as the part number of the manual itself.





    Look further in the manual for the complete parts list.
    Control module and housing 381-330-029
    Display board and housing 381-330-030
    ethicalpaul
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I'm not so sure about the EVG and ECO controller compatibility. The EVG is cascadable whereas the ECO is not. Maybe that's the biggest difference. Also the EVG has a more sophisticated display which is likely the 5th pin you speak of. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    May I point out another possible problem? (sorry...). These are computers. Computers are programmed. You have no guarantee that, even if you could figure out the apparent pin relationships, that the programs on the EVG controller and display modules are compatible with your ECO boiler.

    They might be. They might not, and if they weren't, it would be quite impossible to figure out what malfunctions and errors -- or out of spec. operations -- were occurring.

    Not quite as spectacular as the havoc caused by throwing an engine control module from a gasoline Ford F150 into a diesel Ford F350 (they are, by the way, pin compatible -- but hardly plug and play) -- but close.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Harold
    Harold Member Posts: 249
    I am making one more check on all the ECO pieces. Then I have to find a reliable service person that fully understands the boiler bits and pieces.

    I have traced all the pins inside the controller and where they go for the entire controller. I believe I could make it work. That socket in the upper right corner is the blocking problem. But I need heat now and I am not being particularly successful. I am going to try to find a local contractor that understands.

    Thanks for everyone's thoughts.
  • Harold
    Harold Member Posts: 249
    A post on the solution. Thought some may be interested.

    I put everything back to the initial configuration. I was unable to make it work. I was unable to get my brain to help. I did not really understand the WM instructions. It did not work.

    Finally I was able to get the original installer. He was working on a mountain in remote location in a no-service phone area. He understands the manual. He returned and I got a call from him literally just as I was about to start contacting random heating providers. He came today and worked on the system. Most likely source of the problem was a wide area power loss shortly before the boiler failed. Turned out that one of two sensors on the SS boiler had failed. Not an impressive life time for such an expensive device. I may put in a second surge protector.

    Contractor is trying to find a replacement sensor. No idea when it will be here. Wife really annoyed. But it is clearly not my fault (this is an important point). Two weeks of cold house has been rather annoying for both of us. Three blankets and dashes to the bathroom.

    Thanks for your support.
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    Thank you so much for the update! And I'm very glad you were able to find someone to find the problem and, more to the point, fix it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    The sensors are the same for both the upper and lower trappings I believe. There is a total of 3 temp sensors. Supply (upper), return (lower), and flue (in the polypropylene flue passage). They are all redundant, which means there are two thermistors in each so that if one fails it will lock out the boiler. I believe the lower (return) only uses one of the thermistors as the return temp isnt a safety issue. 

    Depending on which sensor failed, you can swap the return sensor for it and may get heat again. I dont understand what all this screen messed up would have to do with a bad temp sensor though. 

    The W-M boilers are made with as many off the shelf parts as possible with the focus of having fewer parts which are unique. At least that's what my W-M rep said. I've have good luck with the W-M ECO and EVG line. Simple units compared to other mod/cons. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Harold
    Harold Member Posts: 249
    And the excitement of a freezing house continues. Have two portable heaters that migrate daily.

    Purchased a new ECO controller. No discernible change except to my bank account.

    Original installer and I have just not found a problem. I have gone through all of the wiring. Talked to the circulators manufacturer to confirm the green/blue/brown wire markings. They verify the internals can use either wire in the circulator.

    Ongoing lack of expertise on my part. Going through the WM ECO manual has not been understandable. We had a terrible time trying to do what is required to get the boiler controller to work. Still no working. We just could not get the little display unit on the outside of the boiler. I have searched for bad wires repeatedly. Swapped boiler sensors around and overnighted new ones. No change.

    Last night, I actually got the DHW and Heat to run. I do not know what I actually did, but for the first time the boiler recognized both heat paths. I heated some water, and it then started on the heat. I left it running last night to start heating the system piping. This morning the boiler is still heating, but only for a few seconds, and then just continues circulating. Over and over.

    I used a IR thermometer and the ever useful hand to look at piping. The boiler goes up to heat temp, various places on the near piping go up to as much as 60 degrees in the general area, but does feel like any significant flow. This is a large house, but the downstairs is unheated. Floors are concrete.

    I stopped now to the boiler and I noticed new possible problem. It may be at the root of things. This may be where stupid is in full control. One of the AquaMotion circulators has all of its lights on. Neither of us paid attention to the pump. Up rather high on the wall and normally has some display lights on most of the operational time. I have the awful feeling that this is the whole problem. Bad pump. It is running and you can hear it (very quiet).
  • Harold
    Harold Member Posts: 249
    Awful feeling was correct. Bad pump.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Never heard of Aqua Motion. Where did you get it?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • iced98lx
    iced98lx Member Posts: 68
    So in the end, the pump wasn't moving water so the boiler was forced to assume that the loop was up to temp?
  • Harold
    Harold Member Posts: 249
    AquaMotion (one word) makes circulators. They are decent pumps. Quiet and good performance. Variable control.

    The pump was not moving water. Boiler tried to heat. Worked fine for DHW pump, but the pump for heat kept trying without any flow.

    Everything working now. But I have a new $500 controller I that I don't need and a very very annoyed wife.
  • flat_twin
    flat_twin Member Posts: 354
    How did the bad circulator make the display stop working? Is the display working again. Thx

    Solid_Fuel_Man
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Yes, that's my question as well. I've had a no flow situation and the boiler kettles quickly and shuts down with a red screen. Lockout for "supply temp rising too quickly" error. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Harold
    Harold Member Posts: 249
    The boiler did not stop when the heat pump kept on spinning with no actual movement in the piping. Probably just modulated heat until I found it. I never poked around as soon as I figured out what failed.

    Everything seems to be working. Now I am working on getting the Tekmar interfaces to work with CrossManifold controls. I think CrossManifold may have been acquired. I saw a picture that looked really nice on a different site. Better than the original I have. They are a clever design.

    I am working at making sure removing the wires that usually go to the remote valves without destroying the use of common connections. I makes me nervous. I have a real problem understanding the interface specified between Tekmar and CrossManifold. I have some relays CM provided, but together they make a bunch of wires and power.