Boiler over filling
nizmo111
Member Posts: 2
Ok I am trying to troubleshoot a boiler . The system shut off when I went to check the glass tube it was completely filled with sediment. I cleaned it and flushed the system and reset the water level after a day or so the lwco was buzzing very loud the boiler shutdown and the water level was high. I drained the system again and cleaned the probe. Reset the system again and a couple days later same problem . Im thinking the relay in the lwco is bad and not shutting off the auto feed system . So I was going to order a new lwco and replace it . Does this seem like it is the issue or could it be something else .
0
Comments
-
I would first shut off the auto feeder . And check with an electrical multi meter first before throwing money at it ...
There was an error rendering this rich post.
0 -
Do you mean test the lwco with tester . Sorry these boiler are pretty new to me. I am a asc mechanic so im pretty good at running down electrical problems just not a 100% on how to test it0
-
Turn off the valve feeding the auto-fill, and see if the water level does not rise.
Sometimes the valve will be leaking because of foreign particles on the seat, or over pressure will force water out into the wet return, temporarily causing a low water situation, and subsequent refilling. When the boiler is off, and the condensate returns, the boiler is then overfilled.
Alternatively, a leak from a hot water coil can overfill the boiler.—NBC0 -
At some risk of pointing out the obvious... that LWCO which is buzzing is... the LWCO. Which is an essential safety device. If there is a suggestion that it is malfunctioning, unless you have a second, backup LWCO, the boiler is not safe to run until you find out why -- unless someone is there, watching the sight glass while it runs.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Is it possible you have a bypass manual feed valve that is leaking & overfilling the boiler?0
-
When you cleaned the sight glass did you brush into the boiler on the isolation valves ports of the sight glass. If the glass was that dirty there is a good chance that the ports are somewhat plugged and give you a false reading in the glass.0
-
The buzzing is probably the 101 feeder solenoid. I would take the low water cutoff apart and clean it or replace it. The float may have a hole in it. Make sure the pipe connections are clear.
And as @Big Ed_4 said troubleshoot it don't just by parts.
This is an Important safety control.
Hire a pro if you need to0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements