Destined For Failure?

erussell58erussell58 Member Posts: 12

Is this a leak looking for a place to happen? Boiler feed line into equalizer line. 

Comments

  • pecmsgpecmsg Member Posts: 1,573
    Nothing wrong with Pro Press. 

    Now is it the proper fitting for that application?
  • erussell58erussell58 Member Posts: 12
    That would probably be the better question.
  • Steve MinnichSteve Minnich Member Posts: 2,617
    According to Viega, MegaPress is approved for steam. Not sure I would use it though. Threaded fittings allow for movement. 
    Author - Hard Knocks: My Life Inside Boiler Rooms
    PHC News Columnist
    Minnich Hydronic Consulting & Design, LLC
    https://heatinghelp.com/find-a-contractor/detail/minnich-hydronic-consulting-and-design
    erussell58Intplm.
  • EBEBRATT-EdEBEBRATT-Ed Member Posts: 7,544
    edited November 21
    It's not propress it's Mega Press.

    You can have it done good or you can have it done fast.

    What pressure is the steam? 15 psi or less it will probably last a while. Now they have Mega up to 4"
  • erussell58erussell58 Member Posts: 12
    We have just had a new Weil-McLane 88 installed and the installation contractor, when finished, had us at 8 PSI. 
    I had a steam consultant in after the installation and he said it was way too high and adjusted down to 1.5 PSI. 
  • Steve MinnichSteve Minnich Member Posts: 2,617
    If it was set at 8 psi, I’d love to see what the near boiler piping looks like. 
    Author - Hard Knocks: My Life Inside Boiler Rooms
    PHC News Columnist
    Minnich Hydronic Consulting & Design, LLC
    https://heatinghelp.com/find-a-contractor/detail/minnich-hydronic-consulting-and-design
  • erussell58erussell58 Member Posts: 12
    Our first problem was the boiler feed line was installed above the water line... sounded like the battle of the bulge. You should quickly see problem number 2!

  • EzzyTEzzyT Member Posts: 1,050
    I see problem number 2 which is the near boiler piping is all incorrect and needs to be redone.
    Creative Solutions Plumbing & Heating LLC
    Lic #12683
    Co-Owners: Fred Drescher, Jr & Eliezer "Ezzy" Travis
    Marketing & Operations: Dawn Drescher
    201.499.0223
    Follow us on Facebook.
    Check us out on Instagram: creative_solutions519
    Danny ScullySteve Minnich
  • mattyorkmattyork Member Posts: 4
    Can you educate me as to why/where the near piping is wrong? I'm a 30 year warm air guy starting to learn boilers.
  • mattyorkmattyork Member Posts: 4
    Risers not high enough off the boiler surface?
  • ratioratio Member Posts: 2,612
    Welded risers with no swing joints to allow for expansion, takeoffs between risers, press fittings on steam are still rather experimental (IMHO, others may not agree), can't really tell what the pipe sticking down over the boiler is but it seems to have a shark bite cap on it.
  • EzzyTEzzyT Member Posts: 1,050
    As @ratio has said there is no swing joints and the boiler riser take offs need to before the steam main take offs.
    Creative Solutions Plumbing & Heating LLC
    Lic #12683
    Co-Owners: Fred Drescher, Jr & Eliezer "Ezzy" Travis
    Marketing & Operations: Dawn Drescher
    201.499.0223
    Follow us on Facebook.
    Check us out on Instagram: creative_solutions519
  • erussell58erussell58 Member Posts: 12
    Thanks everyone for their help! Does the threaded 4” pipe riser coming directly off the boiler count as the swing joint? The riser is threaded at the boiler take off and the bottom of the flange.
  • Steve MinnichSteve Minnich Member Posts: 2,617

    Author - Hard Knocks: My Life Inside Boiler Rooms
    PHC News Columnist
    Minnich Hydronic Consulting & Design, LLC
    https://heatinghelp.com/find-a-contractor/detail/minnich-hydronic-consulting-and-design
  • erussell58erussell58 Member Posts: 12
    I love page 17 lol... 
    interestingly, We have a 688. Fig. 24, says riser A should be 5” but specifies a (1 riser) Whereas Fig. 25 shows models 788-1188, with Double risers but at 4”” to 5”
    we currently have 4” risers. Seems a bit confusing there. Semantics? 
    Intplm.