Heating the basement
Gigfy
Member Posts: 1
I have steam heat and want to heat my basement . Is it recomended to take hot water from the steam boiler and circulate it through a baseboard system with a circulating pump?
0
Comments
-
That certainly is much the simplest way to do it. If all the baseboard is going to be below the water level in the boiler, all you need to do is find a convenient tap on the boiler below the water line, pipe from that to a pump, then the baseboards, then back to a wet return somewhere. The control can be just a thermostat to turn on the pump -- although you can get fancy and add an aquastat to turn on the boiler to make sure it's hot. Doesn't take much of a pump.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Doesn't even have to be below the water line:
https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yes, if you heat blow the water line , you don't need a heat exchanger to pressurize the column of water . Just to note circulators get eating up with solids left behind . Maintain and repair any steam leaks
There was an error rendering this rich post.
0 -
Even above the water line you don't need a heat exchanger. Broken record mode is on.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements