Thermostat for Hydronic Kickspace Heater
Sparkie212
Member Posts: 11
I installed a Beacon Morris K42 Kickspace heater and it is working as expected. I would like to have it controlled by a thermostat since its in a bathroom and will get to hot without it. The directions call for a line voltage thermostat, but I was having trouble finding one that would work with my unit since the K42 only uses about 30 watts to run the fan, the heat comes from hot water. I would like to use a heat only 2 wire 24 volt thermostat and use a relay like RA89a From Honeywell. will this work or is there a better option? Running electricity for a line voltage thermostat is not preferred. Thanks mark
0
Comments
-
Your option should work. Note that you will have to run a 120 volt circuit -- line voltage -- to the relay anyway, so I'm not quite sure what, if anything, you are gaining. You will still get a little heat from the kickspace heater anyway, but it won't be that much.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I already have the electric in the crawl space run and hooking up a relay would be simple, Running the conduit trough the wall would require a larger hole for the box and then more drywall and painting. I did not know if the RA89a would be overkill or if there was a better option. I have a few of the RA89A's already to control the pumps for my boiler and at times I have a bit of a humm and would like to make sure I install something that is quiet.0
-
plenty of line voltage thermostats available. Look at any of the electric radiant heat manufacturers.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
thanks for the screen shots of thermostats.0
-
I did the installation with a 2 wire heat only thermostat connected to a Honeywell RA89a and mounted the RA89A to a 2 x 12 floor stud and it works fine but I get a humm when activated, I tried putting a piece of rubber behind the RA89A and still get the humm. Is there any way to get rid of the Humm or should I have used a different relay?0
-
Yeah, some transformers make a humming sound, maybe try and isolate the mount somehow.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@Sparkie212
Funny you mention that freiking humming. I had a RA89A on my boiler for 40 years no problem. The relay quit and I bought a new one same thing......looks the same too.
But the new one hums. I read in the paperwork that Honeywell says to mount it on rubber. I ended up changing the boiler and sold the house and didn;t use the relay.
Pisses me off because honeywell has been making those relays for years
0 -
May I say -- drawing on the high fidelity sound side of my life -- that building a transformer which doesn't hum is really remarkably difficult, especially if one is trying to hit a price point.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I did try and isolate by putting rubber behind the relay and no help. Not sure what else would help. The RA89A is in the crawlspace and I can hear it on the main floor. I do have a few real old RA89A's on my boiler and they are not that noisy. The Taco relays say if there is hum they supply resistors that are supposed to help, I dont know if that is possible on the RA89A? Taco is saying that some power robbing thermostats are a culprit. My themostat is not programable but digital also has two batteries. Is there anything I can do to get rid of hum?0
-
Be sure that your mounting for the relay is actually vibration isolating. Just putting rubber behind it won't help -- it's the mounting screws or bolts or whatever. You need to create a mount which has no solid contact whatever between the relay case and whatever it's mounted on. Something like a mounting plate secured to the substrate and the relay secured to the mounting plate with nuts and bolts through rubber grommets in the holes in the plate.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Is this what you had in mind?
0 -
Try temporarily hanging the relay by a wire or something just to see if it eliminates the noise issues to an acceptable level . Suspend it with some perforated plastic plumbers tape
Or get a different relay.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Exactly.Sparkie212 said:Is this what you had in mind?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks for all your help I will try and isolate the relay and see if that helps.0
-
Well I isolated the RA89a and I still get the hum. I got a hold of Resideo(honeywell) and they recommended me sending unit back for refund with no recommendation for replacement. I just assume that relay is going to hum. Any suggestions for another relay or solution to my issue? I saw another relay the Taco Sr501-4- not sure if that will also hum. ??0
-
Hard to predict which transformer will hum, I think it is more about quality, not the brand name.Sparkie212 said:Well I isolated the RA89a and I still get the hum. I got a hold of Resideo(honeywell) and they recommended me sending unit back for refund with no recommendation for replacement. I just assume that relay is going to hum. Any suggestions for another relay or solution to my issue? I saw another relay the Taco Sr501-4- not sure if that will also hum. ??
We had transformers built to a tight output voltage spec for the snowmelt sensors we sold, like this one.
Direct plug in transformers built into a case like this tend to be 100% silent. Typically used for door bells, alarm systems, etc.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I can live with a little hum but the Honeywell seems excessive. The real old Honeywell ones I have are pretty much silent, not so with the new ones
0 -
-
Thats one of the ones I was thinking of replacing it with. If you have a question you can actually get a hold of someone at Taco also which may or may not be helpful. - Thanks for the suggestion.0
-
Replaced with the Taco 501-4 and working just fine, Thanks again0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements