Proper way to get a C-wire.
TheHeat
Member Posts: 7
I could use some help flushing out a C-wire for some smart thermostats.
I have a radiant heating setup with 6 zone valves (4 older Honeywells and 2 Tacos from an addition prior to my moving in). There is also a Honeywell valve for an indirect hot water tank. They are all controlled off a Taco 4-zone controller as pictured: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201024_210022.jpg
Current heating thermostats are two-wire (R and W), but there’s a green conductor as well that I’d like to re-purpose as the common.
The Honeywell valves all appear to gang together and tie to the Isolated End Switch. The newer Taco zone wires connect to the Zone 1 and Zone 2 thermostat and Zone 1 & 2 end switch connections.
Aside from the transformer in the valve controller box and anything that may exist at the boiler, there are two transformers mounted on the wall, also pictured: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201117_212329.jpg. These appear generally wired to the Honeywell circuits. It is only the Honeywell zones I’m interested in converting to use smart stats.
I came across the Taco wiring guide, which shows a couple options for common wiring: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=zone_control_wiring_diagram_1009.0_51.pdf. However, neither exactly reflects my scenario.
The zone valve diagram shows wiring to terminal 1 of the zone 1 end switch. Will this work given Zone 1 isn’t any of the zones I’m looking to have upgraded to smart stats? It also shows a 2-wire connection instead of Taco’s 3. I assume no way to connect to the isolated end switch instead?
The zone circulator diagram shows wiring to a connection point I’m not sure I have unless it means a transformer terminal. Is there some functionality here that would work?
I’ve heard mixed things about connecting to the transformers if not provided with a dedicated common. I imagine this would also apply to the wall-mounted transformers too?
The room: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201117_212347.jpg
Thanks for reading. I appreciate any help you can lend.
I have a radiant heating setup with 6 zone valves (4 older Honeywells and 2 Tacos from an addition prior to my moving in). There is also a Honeywell valve for an indirect hot water tank. They are all controlled off a Taco 4-zone controller as pictured: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201024_210022.jpg
Current heating thermostats are two-wire (R and W), but there’s a green conductor as well that I’d like to re-purpose as the common.
The Honeywell valves all appear to gang together and tie to the Isolated End Switch. The newer Taco zone wires connect to the Zone 1 and Zone 2 thermostat and Zone 1 & 2 end switch connections.
Aside from the transformer in the valve controller box and anything that may exist at the boiler, there are two transformers mounted on the wall, also pictured: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201117_212329.jpg. These appear generally wired to the Honeywell circuits. It is only the Honeywell zones I’m interested in converting to use smart stats.
I came across the Taco wiring guide, which shows a couple options for common wiring: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=zone_control_wiring_diagram_1009.0_51.pdf. However, neither exactly reflects my scenario.
The zone valve diagram shows wiring to terminal 1 of the zone 1 end switch. Will this work given Zone 1 isn’t any of the zones I’m looking to have upgraded to smart stats? It also shows a 2-wire connection instead of Taco’s 3. I assume no way to connect to the isolated end switch instead?
The zone circulator diagram shows wiring to a connection point I’m not sure I have unless it means a transformer terminal. Is there some functionality here that would work?
I’ve heard mixed things about connecting to the transformers if not provided with a dedicated common. I imagine this would also apply to the wall-mounted transformers too?
The room: https://www.dropbox.com/sh/0i2zcbk94sokw1t/AACoytU5z15shwWUineUpF8Ya?dl=0&preview=20201117_212347.jpg
Thanks for reading. I appreciate any help you can lend.
0
Comments
-
-
Thanks! That...makes sense. Can I connect to any of the 4 C terminals? The tstats in need of a C aren't the ones that are wired into the R and W.0
-
Thanks! That...makes sense. Can I connect to any of the 4 C terminals? The tstats in need of a C aren't the ones that are wired into the R and W.Solid_Fuel_Man said:The green can simply be landed on the C connection on the zone valve controller.
R= constant 24 volts
W= call for heat
C= negative or common for the 24volts0 -
-
Yes, that is correct.Solid_Fuel_Man said:The thermostats which you want to upgrade are controlling zone valves which are powered by one of those transformers on the wall in your picture?
0 -
Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
This is what you need to do.
Basically "C" is common to the transformer, valve, and now the thermostat. R is 24 volts straight from the transformer, and w is the call for heat (switch in the thermostat connects R and C when its cold).Serving Northern Maine HVAC & Controls. I burn wood, it smells good!1 -
Thanks Solid_Fuel_Man! Heating advice from northern Maine pro comes highly appreciated.Solid_Fuel_Man said:This is what you need to do.
Basically "C" is common to the transformer, valve, and now the thermostat. R is 24 volts straight from the transformer, and w is the call for heat (switch in the thermostat connects R and C when its cold).0 -
You are welcome!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements