Best way to create small differences in water temperature?
hullabaloo
Member Posts: 9
My radiant design calls for 115 degree water on the upper, very well insulated level, but 125-135 on the main living level, maybe less if we supplement with our mini-split cassettes on the coldest days. Additionally, most of the home will be heated from under the subfloor, but I may heat directly under the tile for the upstairs baths. I know that I can use a mixing valve to have both temperatures on the different levels, but is there a way to get two temps on the same zone? Specifically:
1. Can I use a mixing valve coming off one circuit of the same manifold? I've not seen a diagram where this is tried. The alternate solution is to pull down a little more ceiling and heat the bathrooms from under the subfloor too.
2. I intend to use an outdoor reset system with my Navien NCB-240, and already have that installed. From what I’ve read, I’ll need some sort of intelligent mixing valve (Taco iSeries?), but am not sure if there is a way to enjoy the savings of modulating the boiler temps, but still have the mixing valve adjust water in different zones? Is there a way to program a valve to get a temperature, say, 20 degrees cooler than the other zone?
3. So this seems like a hack idea, but… if two zones could be expected to mostly run at the same time (as they should with an outdoor reset setup, could the cooler zone be plumbed in series with a warmer zone? My system was designed with a 20 degree delta T, so if I ran a “cool” zone off the return water from a warmer zone, could this in theory work? Mostly musing here, since I plan to go with a proven solution for the final design.
1. Can I use a mixing valve coming off one circuit of the same manifold? I've not seen a diagram where this is tried. The alternate solution is to pull down a little more ceiling and heat the bathrooms from under the subfloor too.
2. I intend to use an outdoor reset system with my Navien NCB-240, and already have that installed. From what I’ve read, I’ll need some sort of intelligent mixing valve (Taco iSeries?), but am not sure if there is a way to enjoy the savings of modulating the boiler temps, but still have the mixing valve adjust water in different zones? Is there a way to program a valve to get a temperature, say, 20 degrees cooler than the other zone?
3. So this seems like a hack idea, but… if two zones could be expected to mostly run at the same time (as they should with an outdoor reset setup, could the cooler zone be plumbed in series with a warmer zone? My system was designed with a 20 degree delta T, so if I ran a “cool” zone off the return water from a warmer zone, could this in theory work? Mostly musing here, since I plan to go with a proven solution for the final design.
0
Comments
-
W H O
is saying 135°F supply for radiant?
110°F max, 120°F for special applications!0 -
Depends on the type of radiant @pecmsg.
Try running it all at the same temperature. Or design the higher temp system for a lower temp.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Pecmsg,
I’d hoped to run cooler temps. When I plugged everything into LoopCAD however, it said I’d need 135 to avoid supplemental heat on that level at my design temp of -6. But I have a gas fireplace (currently old and drafty) plus a couple mini-splits on that level (not great at -6F) so I don’t necessarily need to go that hot. The system is staple-up light gauge 4’ heat plates under the subfloor. I hadn’t heard of an absolute ceiling for temps and just planned on easing into it gradually, ideally staying at 120.0 -
AgreedSolid_Fuel_Man said:Depends on the type of radiant @pecmsg.
Try running it all at the same temperature. Or design the higher temp system for a lower temp.
If floor thats too HOT0 -
Could run the secondary in series off the primary. Hottest zone gets water first and the 135 setpoint. The 125-120f then feeds second zone. Water returns are 100-105.0
-
-
Not new construction, just a new heating system. The house is a '67, heated up to now with fin-tube baseboard. I've got two rows of 5" transfer plates in each 16" joist bay, can't really do a third. I will focus on energy loss on that level, and supplement heat if needed. We did a insulation refit on the upper level a couple summers ago were we replaced insulation and added rigid insulation board underneath new siding. The main level is brick however, so fewer options to improve insulation, though I still have some air sealing to do.0 -
-
Thanks Guys. I decided to just run everything on the cooler water temperature and see how it goes. I bought a manifold with an extra zone that can be enlisted for a possible radiant wall on the cooler zone if needed. I also have a few insulation ideas and Will eventually pull out my gas fireplace logs and do a more efficient insert. I don’t think it will be a problem. I should know in a couple of weeks :-)
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements