Debugging/Troubleshooting apparent zone fault
JimM66
Member Posts: 4
in Oil Heating
My system:
Buderus boiler controlled with a Logamatic 2107, Taco SR503 switching relay. 2 heating zones and DHW, each with it's own Taco 007 circulator pump.
I noticed that one of the heating zones was colder the other morning when outside temps dropped to the high 20s. The thermostat's batteries are good, and the zone LED on the SR503 is lit, but the circulator pump isn't running. Let's call this Zone 1.
Since my other heating zone is working as expected (let's call this Zone 2), I swapped each of the following (bad zone<->good zone):
When the Zone 2 thermostat called for heat, the Zone 1 circulator pump started operating.
When the Zone 1 thermostat called for heat, the Zone 2 circulator pump did not start operating.
It's clear that the circulator pumps aren't the issue.
It's clear that the thermostats aren't the issue.
It's clear that the relays are good.
The wiring is good.
I'm placing a call to my home heating professional in the morning - just wanted to ask here what your opinion on the problem might be so as to prepare myself for the professional's diagnosis.
Buderus boiler controlled with a Logamatic 2107, Taco SR503 switching relay. 2 heating zones and DHW, each with it's own Taco 007 circulator pump.
I noticed that one of the heating zones was colder the other morning when outside temps dropped to the high 20s. The thermostat's batteries are good, and the zone LED on the SR503 is lit, but the circulator pump isn't running. Let's call this Zone 1.
Since my other heating zone is working as expected (let's call this Zone 2), I swapped each of the following (bad zone<->good zone):
- Thermostats - no difference in operation (Zone 1 still doesn't enable its circulator pump, Zone 2 still normal).
- 24V relays - no difference in operation (Zone 1 still doesn't enable its circulator pump, Zone 2 still normal).
When the Zone 2 thermostat called for heat, the Zone 1 circulator pump started operating.
When the Zone 1 thermostat called for heat, the Zone 2 circulator pump did not start operating.
It's clear that the circulator pumps aren't the issue.
It's clear that the thermostats aren't the issue.
It's clear that the relays are good.
The wiring is good.
I'm placing a call to my home heating professional in the morning - just wanted to ask here what your opinion on the problem might be so as to prepare myself for the professional's diagnosis.
0
Comments
-
You say that you are sure the thermostats and their wiring aren't the problem, but as I read your post I see this: Zone 1 thermostat connected to zone 1 circulator, no joy. Zone 2 thermostat to zone 1 circulator, good. Zone 1 thermostat connected to zone 2 circulator, no joy. Zone 2 thermostat connected to zone 2 circulator, good.
Am I missing something? Or confused? From that I would look at the zone 1 thermostat or its wiring?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Maybe I didn't do the best job describing what I did.
Both thermostats called for heat on Zone 2, and the circulator pump on Zone 2 started up.
Both thermostats called for heat on Zone 1, the Zone 1 LED on the SR503 lit, but the circulator pump on Zone 1 did not start.
Setting the thermostats back to their original positions, I then swapped the wiring inside the SR503.
Both thermostats, when calling for heat on Zone 1, saw the Zone 1 circulator pump start.
Both thermostats, when calling for heat on Zone 2, did NOT star the Zone 2 circulator pump.0 -
ControllerBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Do you have a voltage meter? You need to check if the transformer is putting out 24 volts. You also need to be sure you have 120 volt power to the pump relay as well as a reliable neutral. From there, do you have power to the load side of the relay?
A quick check for these is to jump the t-stat terminals."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Heating professional came today - diagnosed the problem as a faulty SR503.
There is some intermittent fault with the controller, as he was able to get the faulty zone operating (evidenced by the circulator pump activating) by re-seating the relay head. But if he touched the head, the pump stopped. There is something amiss with the contacts for the relay head within the SR503 (he swapped in a known good relay head, so we know it's not the relay head).
New SR503 to be installed.
Thanks for the input!
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements