So Im a building superintendent living at the building Im managing. Currently renting out my two family My current boiler 45 yr peerless 120. oil fired steam one pipe system heats the second floor of Two family home built 1925 second floor flat has 6 radiators only one really big one , the apt is 986 sq ft , both porches 3 season. I put in contractor windows in 98 . There is an old 7 inchs of fiberglass insulation in attic being gone over with 13" of new from home works - soon. I joined this forum last week , very impressed with the knowledge of here I look forward to your advice over the next week or two or 3?
my last oil man told me to get a new oil boiler a couple of years ago because of the ineffecincy

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,564
    Your question is "can a steam boiler be run successfully with gas?"

    The answer is hell yes. I personally like gas because it can be a LOT quieter, a bit cheaper, and you don't have to have a smelly hazardous substance stored on your property refilled every heating month. Oil people will say that oil doesn't explode, but neither does gas with a minimum of competent installation and maintenance.

    It seems like you might have a whole lot of other questions in there but I admit I couldn't parse them out.

    I will add that it's vital when replacing an oil or gas steam boiler that you size it to *your installed radiation*! Not your insulation, not your sq feet of space, not how many bedrooms, and definitely NOT the size of your existing boiler!

    Come visit the Strictly Steam subforum and look at pictures of nice installs and people asking questions similar to yours.

    https://forum.heatinghelp.com/categories/strictly-steam

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    bleeder
  • mattmia2
    mattmia2 Member Posts: 10,841

    Oil people will say that oil doesn't explode, but neither does gas with a minimum of competent installation and maintenance.

    I have a distant cousin that was an insurance adjuster. He said he has seen lots of claims for fires from oil. The only claim he saw for gas was from someone who had intentionally disconnected some piping in a suicide attempt.

    ethicalpaulbleeder
  • Jamie Hall
    Jamie Hall Member Posts: 24,724
    Neither oil nor gas is dangerous, properly installed and maintained. Both of them can cause difficulties, shall we say, if not properly installed and maintained.

    If you can smell oil in the property, you have a leak somewhere; it wouldn't be such a bad idea to take some time and find it. If you can seriously smell oil (that nice diesel smell we used to like!) outside, the combustion settings on the burner are way off.

    If you can smell gas, don't touch any switches for anything and leave the premises. Then call the gas company and fire department.

    A much more pertinent consideration is -- can you get gas at all? And if so, how does the price per BTU compare with oil? In some areas, this may make one or the other non-competitive, or simply a non-starter.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,397
    The first day of school the instructor told us if there was a problem with oil you remodel, with gas you rebuild LOL
    I would go gas and get rid of the oil tank
    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,309
    edited September 2020
    I have a question about the fact that the building is a 2 family. How is it divided... up and down or side by side?

    Next... if side by side, are there 2 different main feeders to the radiators? (one for each side)

    If properly separated, you can use 2 smaller gas boilers and run them from separate gas meters. Separate water heaters might also be easy. Then separate gas cooking. Now you don't need to pay for someone else's heating bill.

    Do that before you move back and get a lower fuel bill for when you do move back home. A good steam man would need to look at this to tell you if it is feasible.

    Oil is out of the question for separate heat, a second tank, boilers are more expensive and may not be small enough. Gas boilers do come in smaller sizes than oil boilers.

    Just an Idea
    Ed

    P.S. if it is an "up and down" duplex, I must take a quote from Emily Litella... "NEVERMIND"



    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 10,841

    The first day of school the instructor told us if there was a problem with oil you remodel, with gas you rebuild LOL
    I would go gas and get rid of the oil tank

    Was that when gas was carbon monoxide and didn't have an oderant?
  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    Been living in the two family up and down all my life until bought from dad condo 1st floor own second floor 7 yrs ago I became a live in sup in boston -free condo so im renting my 2nd floor apt,
    1st floor heats with gas and 2nd floor upstairs we use oil always have and I have never smelled oil in all the years living there, well cared for peerless has treated us right. But lots of oil use its burns oil like there no tomorrow I had a new line from tank put in 15 years ago could of sworn it was leaking out underground but that didnt change anything my oil co says its time for new boiler (oil man) my brother the service man moved to Maine says its old but should be at 82- why wouldnt it be, I was filling the water once a week then had new steam valves put on oil co put in automatic feed and it cut the water use down to

    * year to date 16 gallons of water - 900 gallons of oil and 12 months hot water also. not a cold winter , not a lg apt..

    I think she is burning to hot set at 160 water controls are old. thats why I need an electric water tank for storage 40 gal in summer if I stay with oil.
    Still havent decided leaning tords gas to get tank out tank is 50 years old
  • bleeder
    bleeder Member Posts: 30

  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    .

  • bleeder
    bleeder Member Posts: 30

  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    she used 900 gallons year to date  it was particularly not very cold of a season
  • Snowmelt
    Snowmelt Member Posts: 1,425
    I sent you a message, but we can size it up be radiator sq ft of steam and get a tankless coil in the new boiler just like you have now or put in a 40 gallon water heater. I have a company that I work with that takes out oil tanks.
    George
  • mattmia2
    mattmia2 Member Posts: 10,841
    That soot, if it is still happening is definitely not helping your efficiency, if it were cleaned and tuned properly that would make it a fair bit more efficient.
  • HVACNUT
    HVACNUT Member Posts: 6,298
    Stay with oil and get the MegaSteam. IMO. The JOT was a decent boiler for its day, up until '83 when they had serious block recalls. Even the replacement  blocks where super tight. 
  • bleeder
    bleeder Member Posts: 30
    must be old soot burning clean flame
  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    .
  • motoguy128
    motoguy128 Member Posts: 393
    FWIM the header could use to be changed when you replace it.  Both supplies off the boiler should come together, then the headers are connected, and finally there should be an equalizer pipe to the return.  Because of all the vertical height you are having any issues.  But it can be changed to provide dryer steam.  
  • bleeder
    bleeder Member Posts: 30
    I know venting is very important. The system looks like it just has those two steam valves you see up top is that enough ill send more pics of pipes
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Good bleeder do you think you can do this yourself, or do you think you just need someone to guide you in the right direction.
  • JUGHNE
    JUGHNE Member Posts: 11,268
    Is the picture of the attic because there are some steam pipes up there or just to show the lack of insulation?

    It looks as if you still have knob and tube wiring in the attic.
    The single conductor hanging on insulators (knob) shows that.

    The knob and tube system must not be covered with insulation.
    The insulation company should be aware of that and report it to the homeowner. They should be concerned with some liability issue for this.
    The joints on K&T wiring are usually soldered and taped. The wire is typically undersized for the over current protection applied. This is allowed because they are considered to be in free air for cooling the conductors.

    IIWM, I would rewire the entire attic because even the next generation of wiring of "Romex" has overheating problems in insulation. Especially at the light fixtures where the heat of incandescent bulbs has been transferred thru the copper wire to the joints of the Romex. I have found bare copper in boxes where this is an issue, as the insulation has baked off. Close to the fire department being needed.

    So another landlord (deductible BTW) upgrade is needed.

    And you need larger new steam main vents.
    luketheplumber
  • mattmia2
    mattmia2 Member Posts: 10,841
    The heat from the fixtures is why sometime in the 80's romex transitioned from the internal conductors being type 60c t or tw to being 90 c type thhn.
  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    I had an electrician give me an estimate on removing all the Knob and tube wiring last week, Im having this done prior to insulation installed-
    Im making notes about the header and equalizer to go over with installer when time comes, this is great knowledge I am receiving and appreciate. Same about needing the larger vents,thx

    Incandecents are gone but boy does it get hot in attic having vents put there as well
  • mattmia2
    mattmia2 Member Posts: 10,841
    edited September 2020
    i don't understand how you would replace the k&t without entering the dwelling a lot.

    Is that an old pipe for gas lighting?
  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    the electrician is a separate contractor who enters the house, the home works company / national grid is the company not wanting to enter the house thru the hatch or stairs.
    and yes very observant old gas lite

    More photos:







  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    Im trying to show the pipes in these photos like in a recent one it was discovered to lower header
    also disregard the photo of the burnham gas boiler next to the peerless that is for the 1st floor unit
  • bleeder
    bleeder Member Posts: 30
    edited September 2020
    .
  • Steamhead
    Steamhead Member Posts: 17,361
    bleeder said:

    my oil co dosent want to install burnham MS they say its a terrible boiler they are always taking them out, they want to install a williamson boiler I said no, burnham or Mclein

    They must prefer less-efficient boilers, for obvious reasons :s
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 6,564
    Williamson is Weil-Mclain but I would never let an oil company tell me what to install.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • bleeder
    bleeder Member Posts: 30
    i hear ya there I will not be letting them do the work, there sizing is by what was there and nothing else. I found a good steam man through the wall that I have actually known for years. I meeting him at the property tomorrow
    mattmia2ethicalpaul