High liquid press/low amps
Banjo_Jim
Member Posts: 6
3T Kenmore (sears) R410 16 SEER central unit, FL 14A, 5 years old
Pressure and amp numbers from Tech (as I remember). I can take temps with IR gun. Ambient temp 80d-60%; condenser temp 80in/110out, lots of air flow; at condenser high side >500psi-82d, low side 110psi-62d; at evap liquid line 85d (both sides of filter/drier), low side 55d sweating; condenser amps are <6A; return air 75d, supply air 60d
Evap coil replaced 3 months ago due to loss of refrigerant. Worked OK until mid-August when a loss of cooling and end to end frozen suction line was observed. Tech recharged using weight and sub-cooling temps (he said, I don't have gauges) and installed UV indicator before a return trip next week. He is concerned the high head pressure indicated a failing compressor. I maintain a failed compressor cannot cool the house with normal values everywhere except a high head pressure and be failed/failing. Does not make sense. Any ideas? Thanks for reviewing.
Pressure and amp numbers from Tech (as I remember). I can take temps with IR gun. Ambient temp 80d-60%; condenser temp 80in/110out, lots of air flow; at condenser high side >500psi-82d, low side 110psi-62d; at evap liquid line 85d (both sides of filter/drier), low side 55d sweating; condenser amps are <6A; return air 75d, supply air 60d
Evap coil replaced 3 months ago due to loss of refrigerant. Worked OK until mid-August when a loss of cooling and end to end frozen suction line was observed. Tech recharged using weight and sub-cooling temps (he said, I don't have gauges) and installed UV indicator before a return trip next week. He is concerned the high head pressure indicated a failing compressor. I maintain a failed compressor cannot cool the house with normal values everywhere except a high head pressure and be failed/failing. Does not make sense. Any ideas? Thanks for reviewing.
0
Comments
-
-
I agree he is scratching his head, but how about a hint of what you think is going on. Technically.0
-
How can you work on anything without gauges?!?!Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
Thanks for that. I am the homeowner trying to resolve the thought the compressor is bad giving you the info I have available.0
-
Ya know, critics are a dime a hundred. Thinkers? Now you got something.0
-
-
-
-
Ironman said:With almost 50* sub cooling, I'd say it's severely over-charged and/or non-condensibles are in the system.
How did he know what the sub cooling was without gauges?
Maybe I misunderstood something when I read the original post?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
I'm thinking it was never evacuated properly or improperly brazed during the coil replacement. Non condensibles or plugged TXV are causing high head pressure. I agree that you need a new tech. At least make sure the condenser coil is clean. It can't be good for the compressor to run under those conditions. Sounds like another piss poor2
-
-
-
I agree with all who say contaminated refrigerant/non condensables. The position taken by you, Ed and others is what I will bring to my warranty service Tech.unclejohn said:Except of course no one on this site would ever dump the charge. What Ed means is reclaim the refrig. and replace the dryer and pull a deep vacuum and weigh in charge.
0 -
Last question; is there anything in the discussion that would indicate a compressor failure or need to replace the compressor? Based on my available data.0
-
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements