Hi, i have a 2 story house with a boiler, water baseboard heat and indirect water heater. The boiler's MAWP is 50psi and it has a 50 psi blowout valve.
People say to run the boiler at 12psi cold and less than 20 when hot. So would it cause any issues if the system is run at a higher psi? Are there any advantages of running at a higher psi e.g. 30psi? Thx.
People say to run the boiler at 12psi cold and less than 20 when hot. So would it cause any issues if the system is run at a higher psi? Are there any advantages of running at a higher psi e.g. 30psi? Thx.
0
Comments
-
Why the 50 psi relief valve? Are you sure it’s not 30 psi relief valve?
Should be a 30 psi, and you probably only need 12 psi cold.
No way should you run that system anywhere near 30 psi.
Fill valve, expansion tank (if bladder type), and system should all be the same presssure.There was an error rendering this rich post.
0 -
-
Fill valve is 12 psi. Just out of my curiosity, so any psi between 12 and 50 is ok? Would higher psi do any harms?0
-
-
Check the rating label on the boiler. It will show the boiler's maximum allowable working pressure. For the record, I have seen hot-water boilers rated 50 lb. MAWP.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
Running the higher pressure has no real advantages and quite a few disadvantages. The risk of leaks is higher, you also need to be sure the expansion tank is rated for the higher pressure and sized correctly for the higher pressure."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
The minimum cold pressure setting is the pressure that you need + a safety pressure of 2-3 psi to expell water from the highest radiator or heat emitter in your home. 1 psi of pressure will hold a column of water up 2.31 feet. So for example, if you measure the distance from the top of the highest rad to the gauge and that distance is 23.1 feet then the cold fill is 10psi + 2-3 psi. A cold fill of 12 psi works for most 1or 2 story homes. Note that the boiler pressure setting has no affect on boiler performance.1
-
@retiredguy nailed it. If your boiler is rated for 50 psi then is able to be installed in the basement of a 5 story building. If the top radiator was 50 ft above boiler pressure gauge you would need about 24 psi of "Static Pressure" in order to force the air out of the top radiators. 24 psi cold water is too close to the standard 30 psi rated for most residential boilers. The relief valve may discharge regularly in that case.
Since you have a 2 story home you don't need the extra pressure. If in the future, you need to replace the relief valve, a 30 PSI would probably be just fine.
Water pressure has no effect on performance in your heating system as long as it is at least high enough to get the air out of the top radiators (like 12 PSI Cold fill pressure)Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
The 50 psi relief valve could have been installed by someone who was having trouble figuring out why the 30 psi relief valve was dumping.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thx. Guys. I learned a lot. Appreciated.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements