AC T-Stat Won't Accept New Lower Setpoint
D107
Member Posts: 1,906
Honeywell RTH221B1021. Installed 2012. The other day I decided to lower the setpoint from 80 to 78 degrees. T-stat still maintains 80. I checked the batteries which are OK. Can't figure this out unless this t-stat has some kind of faulty resistor etc. Never had a problem before. I will try other T-stats I have lying around if this thread doesn't come up with some solution that I'm missing. I see it has three wires.
0
Comments
-
-
Well, thermostats do fail -- but not usually so they refuse to change setpoint.
So -- I presume you have checked the obvious? That, in fact it does turn off the AC when the temperature drops to 80, rather than keeping going to 78? Place a reliable thermometer right next to it, to verify that the display isn't lying to you.
Then run a second quick test: turn the setpoint up -- say to 85, assuming it's warm enough for the building to reach that. Does it still lock on and hold 80, or does it allow the temperature to rise before kicking on? And if it rises, rise to what?
Assuming it passes that, now a third test: from 85, which it now holding, wait until the thermostat shuts off the AC, and then drop the set point to something much lower -- say 75. After a short pause, the AC should kick on and keep going until it gets down to 75 -- and then shut off. But watch out for this test: it's possible that the AC system won't shut off, but that the temperature doesn't get down to the set point. That's not the thermostat's problem; that tells you that the AC doesn't have the capacity to get down there. And if the AC does shut off, but the thermostat display still indicates it's above the set point, make sure that it is the thermostat that has shut off the AC, rather than the AC itself.
And tell us what has happened...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Is the thermostat set to "Hold" to bypass the program . If not the set point you set is temporary .. the program set point could be set to 80* at different periods
There was an error rendering this rich post.
0 -
-
@ratio @Jamie Hall @Big Ed_4 @ChrisJ Just got home and checked it out. Wasn't on Hold but it's been so long since I'd re-set this I had forgotten that this has four different period settings. So I changed all four set points, but first time it still went off at 80, but interestingly the 'cooling' notice was blinking, indicating the t-stat was calling for cooling but AC unit was off.
Then I turned unit off and re-started, now it seems to be cooling down on its way to 78. Will see if this maintains. If not I'll go through all of Jamie's list.
(This is straight AC, 3 ton 1989 unit, usually no problem bringing it down to 72 even at 90 outside temp.)
This T-stat is one that will always show the set temp as the actual temp--which I like. So if it's set to 78, when it gets to 78.5 or whatever the tolerance is it still shows 78 then AC kicks in, and when it gets down to whatever the differential is 78? 77.5? it will still show 78.
Thanks for all the trouble-shooting tips--I'll copy them and save them for the future. Since I'd just re-set the other three periods to 78, perhaps it needed a little time to re-sync with the unit to put that into effect. Note to Self: Always read the directions again!0 -
-
-
-
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements