System 2000 runs for a minute, shuts off stays off for a couple minutes and then runs for a minute
grumpy47
Member Posts: 5
My System 2000 is quiet but for the last year or more it short cycles. I live in a duplex with two separate zone valves, Honeywell ditigal. I have had two local boiler guys look at the problem. The guy suggest staggering the time the thermostats come on. The other guy didn’t know what to do. So the problem still exist. Once both sides of the duplex quit calling for heat the furnace stops. Bypassed the system manager with a green card but didn’t solve the problem. Installed new fuel pump still cycles. Checked both thermostats to see if they worked separately all good. Both turned off the furnace when I set the thermostat to stop calling for heat. The greatest fraustration the guy who installed at least 10 years ago retired and have not found someone to help with the problem. Any advice would be greatly appreciated.
0
Comments
-
It's only during heating calls? Not domestic calls?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Year or more...? Someone from EK will probably be by shortly for guidance.
There was an error rendering this rich post.
0 -
another thought..have someone call energy kinetics while sitting in front of the equipment..0
-
Thank you for your question, @grumpy47 .
I’m guessing you mean the “burner” runs for a minute and then shuts off for a few minutes.
If this is the case, it sounds like a flow issue on the boiler side, possibly a bad circulator or other blockage. Surprisingly, gravity flow can sometimes provide enough heat to satisfy thermostat calls.
If the burner turns off while the burner light on the manager is on, it could likely be a boiler side flow issue.
We welcome a call from your heating professional to walk through the symptoms and develop a resolution. It’s especially helpful if they call from your duplex.
Best,
RogerPresident
Energy Kinetics, Inc.4 -
Hi Roger, So appreciate your reply. The main problem here in Alaska I have not found a knowledgeable professional. I had them on several occasions change out the circulator pump on the heating side and also the aquastat. What is so interesting when I take a shower everything runs normally. The temperature is 170 then drops to 150 the burner turns on and runs for around 4 minutes. Did this twice while taking a long shower. So I would assume this is normal. But when I turn up the thermostat the burner runs for a minute and shuts off.0
-
post a picture of the near boiler piping including to the domestic tankknown to beat dead horses0
-
Thanks Roger, I have two zone valves for my duplex. I can check it again but I think the burner cycles regardless of what side is calling for heat. I can’t check now because I have a bypass green card to operate the burner bypassing the manager.0
-
We should get more details while operating the system, and maybe we can talk with your heating professional first to explore other ideas. It sounds like the temperature limit may be turning off the burner, which it’s typically a boiler side flow issue.President
Energy Kinetics, Inc.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements