Weil McLain cga 5
Snowmelt
Member Posts: 1,420
I have a 3 year old cga that I am taking out of a customers house. Like I said irs only three years old, one of my friends wants it but it’s just a little bit oversized. What’s involved in reducing the gas input/ output? Is it as simple as blocking off a burner. Is that going to effect the flow size? Hypothetical the existing boiler is 102 output and I only need 75, how would you go about doing this?
0
Comments
-
You cant. And really should not. Boiler is designed to run w/ the orifices' provided. By you messing w/ that you could get sooting and excessive CO.
0 -
Ok thanks, what about lowering the W.C in the gas valve?0
-
Same. The boiler was tested at 3.5" manifold pressure with all the burners. You mess with it, it's on you.0
-
If you're putting it in a high mass system...ie radiant floor or gravity conversion... the extra capacity really shouldn't be a problem. If you're running low mass, IE fin tube baseboard... then I might have a concern, especially if zoned.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
I would not even worry about the over size other than fuel cost. Can't tell you the number of times I have seen boilers way over sized. I have taken 250K out and put 140K in.0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 886 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements