Mitsubishi Indoor/Outdoor Problem - One room never stops cooling - Problem Solved
The outside is MR Slim R410A Model MXZ-4B36NA.
On the inside, I have 1 18,000 BTU unit for the downstairs, and 1 9000 and 2 6000's for the bedrooms upstairs. I know it's a little overloaded, but I rarely ever have all 4 units on at the same time.
I have problems with the 9000 in the master restroom and one of the 6000's in one of my daughters rooms. The 9000 seems to get stuck in "Dry" mode, when it is set to be in "Cool" mode. The bigger problem is the 6000.
The first issue with the 6000 is that "sometimes" it freezes the room out. I'll go in there and its set on 69 degrees, but the room is 59, and the AC is still on. The second issue with that unit is that when the downstairs unit is on, the 6000 upstairs is dripping water out of the drain like it is running, which it is not, it is off, with the flaps close and no fan running. I can feel something is going on inside it because it is very cold inside the unit.
Does anybody have any clues on what might be going on with that 6000 unit? Is it normal behavior? It sound to me like the other units (on one other unit) are affecting the 6000. The contractor that installed them never returns my calls. I get they are very busy, but basically we have been abandoned.
Comments
-
Unfortunately, you're gonna have to find another contractor. One who knows what to look for or get tech support on the line.
Where are you located?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Lebanon, NH0
-
Try the contractor locator above.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Ok. Thanks0
-
-
Even though one head is off while others are running, the system can route refrigerant through the "off" head evap to keep the pressures correct.
The 59° room is something else. I'm not too familiar. Are they simple remotes for each head or does each head need to be addressed?0 -
Sounds like a oversized “System” it’s trying to maintain temp but can’t turndown enough so allows refrigerant To bypass to the other heads.
Agreed need a knowledgeable tech and Tech Support0 -
That is good information. Thank you
What do you mean "does each need to be addressed"? Each head has its own remote.0 -
"Sounds like a oversized “System” it’s trying to maintain temp but can’t turndown enough so allows refrigerant To bypass to the other heads. "
I don't think the system is oversized. I'll look into that. I trying to schedule a contractor, but nobody is returning any calls, exactly they same experience two of my neighbors are having too. This area is must be severely backlogged.
0 -
HVACNUT,
Do you think this is possible? Like you say, the system may be routing refrigerant to that 6000BTU head to keep the pressures correct, BUT not only when off, but when the room is at the right temperature, and because my system is programmed to run the fans 100% of the time, it continues to cool the room way below the set temperature?0 -
Put the fans to “auto”.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The very first thing I would triple check is making sure all the interconnecting wiring is correct. I just found a multi zone system earlier this summer where 2 of the zones had the wiring swapped. It ran like that for 3 years without being noticed, until a new tenant moved in and switched the 1 zone off. The one zone was freezing up without the blower running.0
-
That has been my theory from the start, but was assured that was not the case, by the contractor over the phone. I will revisit that. Thank you.wesPA said:The very first thing I would triple check is making sure all the interconnecting wiring is correct. I just found a multi zone system earlier this summer where 2 of the zones had the wiring swapped. It ran like that for 3 years without being noticed, until a new tenant moved in and switched the 1 zone off. The one zone was freezing up without the blower running.
0 -
You might try tracing it yourself. You have much more time and knowledge of your particular system than a tech will have.rick25s said:
That has been my theory from the start, but was assured that was not the case, by the contractor over the phone. I will revisit that. Thank you.wesPA said:The very first thing I would triple check is making sure all the interconnecting wiring is correct. I just found a multi zone system earlier this summer where 2 of the zones had the wiring swapped. It ran like that for 3 years without being noticed, until a new tenant moved in and switched the 1 zone off. The one zone was freezing up without the blower running.
0 -
The first few things to check are the wiring & the piping, make sure nothing's crossed. It happens. After that, think about your usage. Sizing is important, but if you're turning heads on & off (or way up & way down, same) you could run into issues, especially if the heads aren't sized to the rooms (that's separate from sizing the outdoor unit). Is this a heat pump, or heat recovery?0
-
It'a a Heat Pump. The one thing I do know for sure is that the heads are correctly sized. I just measured each rooms cubic feet and the installed head sizes are right in the middle of the range. I do no leave them on 24/7. I turn the downstairs one when I start my workday from home....covid style. I turn that one off at about 9pm. I turn bedrooms ones on about 6pm and they shut down at around 6:30 am.ratio said:The first few things to check are the wiring & the piping, make sure nothing's crossed. It happens. After that, think about your usage. Sizing is important, but if you're turning heads on & off (or way up & way down, same) you could run into issues, especially if the heads aren't sized to the rooms (that's separate from sizing the outdoor unit). Is this a heat pump, or heat recovery?
0 -
Heat loss/gain is sized via a Manual J survey, not by square feet. It's possible they're close enough, but since we're having trouble, the sizing of the heads is still questionable.
Your outdoor unit will give you a max of 36k BTU/H of cooling. You've got 18K of load on the first floor and 21K on the second floor. Sounds like you basically run the downstairs or the upstairs, with a few hours of overlap. Several second floor units overcool when the downstairs unit is operating.
Your outdoor unit is oversized for your usage pattern. Try setting all the heads to maintain 72° with no setback & see how the system performs. Leave the fans in auto so the system can manage them as well.
1 -
I'll give it a shot. Thanks.0
-
Here is the results overnight. I set them all on "cool" at 72, with the fans on automatic (as always). These were the room temps at 6:30am.ratio said:Your outdoor unit is oversized for your usage pattern. Try setting all the heads to maintain 72° with no setback & see how the system performs. Leave the fans in auto so the system can manage them as well.
18,000 BTU Downstairs: 72
9,000 Master bedroom: 72
6,000 Bedroom 1: 72
6,000 Bedroom 2: 580 -
Hmmmm... Now that looks like something going on with the 6K head. Everywhere except the second bedroom is comfortable now? I don't suppose you can check the programming in it & compare it to the other one? Did you notice any trouble meeting setpoint during the heating season?
Are these heads piped all the way back to the outdoor unit, or are they manifolded together somewhere?
0 -
The EEV might be stuck open, or the solenoid valve at the outdoor unit.
You'll need a pro to check, along with resistance readings on multiple thermistors, verified by Mitsu tech support, file a claim, order part(s), yadda yadda yadda.
Call the contractor back and make an appointment. You weren't abandoned, it got busy, quickly. Most of the trades are backed up.0 -
What size bed rooms per size heads ?
There was an error rendering this rich post.
0 -
I have no idea how to check the programming. I'm capable but never ran across a service manual. It seemed to heat fine, but I can't remember completely. All I can say is I didn't notice a problem heating with that head, but our main heat could have covered for that.ratio said:Hmmmm... Now that looks like something going on with the 6K head. Everywhere except the second bedroom is comfortable now? I don't suppose you can check the programming in it & compare it to the other one? Did you notice any trouble meeting setpoint during the heating season?
Are these heads piped all the way back to the outdoor unit, or are they manifolded together somewhere?
All the heads are piped back to the outdoor unit. I just confirmed it.0 -
Yes, I get they are busy, but I started trying to get an appointment in August 2019. I was finally able to get an appointment for Friday. We'll see if they show. All the info from you guys made it so I can articulate the problem to them better.HVACNUT said:The EEV might be stuck open, or the solenoid valve at the outdoor unit.
You'll need a pro to check, along with resistance readings on multiple thermistors, verified by Mitsu tech support, file a claim, order part(s), yadda yadda yadda.
Call the contractor back and make an appointment. You weren't abandoned, it got busy, quickly. Most of the trades are backed up.1 -
Guess what? The service tech I had an appointment with Friday.....Never showed up, never called, never anything.
After taking in everything everybody here is educating me about, this is what I notice. No matter what units are on in the house, the 6000 I speak of has coolant running through it, whether it is ON or OFF. It is freezing out the room because, when it is ON, the coolant is still being delivered to it whether the room is at temperature or not. So while the fan is running (automatic setting), refrigerated air is being pushed into the room. There is no way to stop the cooling other than turning the unit off. My only option is to program the remote to turn the unit to turn off at 1am, when the room usually hits 62 degrees (set at 72), which is not really a solution.0 -
It does sound like something going on with that head. I'm sorry the tech didn't show up, did you try the "find a contractor" link at the top of the page?
I haven't studied this particular unit, but all the VRF units I know of, including Mitsubishi commercial systems, never close off refrigerant to a head completely—it must remain open a little for oil control. I believe you can program the head to turn the fan off completely. Thought I'm not convinced this is the source of the problem, it should help a little.
0 -
Sq Ft of the bedrooms.
If it was sized properly all 4 heads should be running nonstop in this heat wave with very little ramp-down!0 -
Sorry to hear about that. No way that should happen unless it was a real emergency. Unfortunately IMO this can't be fixed here. Contact Mitsubishi and tell them what's going on with your experience with their equipment. They should have a list of certified dealers and play middleman in hooking you up with a contractor that can help. Have them do a 3 way call and nail down a date. There are plenty of service vehicles driving around with Mitsubishi splashed on it and Mitsubishi should want reliable service for their product.2
-
Not in the upper valley of NH. It's a commerce wasteland here. I have called Mitsubishi, and they tell me the call needs to originate from a contractor. None of the contractors they gave me returned any calls or emails.HVACNUT said:There are plenty of service vehicles driving around with Mitsubishi splashed on it and Mitsubishi should want reliable service for their product.
I just looked back through my notes, and I have been trying to get this fixed for 14 months.
I appreciate all the advice.
0 -
Too Large!rick25s said:
8ft ceilingspecmsg said:Sq Ft of the bedrooms.
If it was sized properly all 4 heads should be running nonstop in this heat wave with very little ramp-down!
9000 BTU: 373 sqft
6000 BTU: 170 sqft. -problem room
6000 BTU: 196 sqft
a 6K head with decent insulation should handle 500Sq Ft + or -
A ducted model should have been used for the smaller rooms.
What's happening now during this heat wave, heads ramping down to minimum?0 -
We had a Mitsubishi head that would turn the room into a freezer. The issue ended up being an installer-issue, in that when they were hanging the head they put a much larger than needed a hole in the wall and never sealed it - this caused the air-temp sensor to never be satisfied since hot air would just pour in through that hole.
0 -
That is interesting.DJDrew said:We had a Mitsubishi head that would turn the room into a freezer. The issue ended up being an installer-issue, in that when they were hanging the head they put a much larger than needed a hole in the wall and never sealed it - this caused the air-temp sensor to never be satisfied since hot air would just pour in through that hole.
I finally got a tech here. He checked all the wiring and piping. All was fine. He was able to reproduce the problem, and called tech support. Tech support said they knew what was going on (which they didn't expand on) and said putting in an MHK remote thermostat will fix the problem. ....we'll see, I guess.
0 -
Problem Solved
The MHK2 remote, didn't alone, fix the problem. I looked at the circuit board (and my electronics technology textbooks from college in 1988) and researched all the labels on the board. I found that there are a couple resisters that double as jumpers controlling the fan. The ones relevant to my model (MSZ-GL) were the jumpers (resisters) labeled JRRE (cool) and JR01 (heat). I contacted Mitsubishi support and they confirmed I was on the right path. The solution was to clip the jumpers off the board. I did this and everything works perfect. The fan shuts off when the set temp is reached, and the room does not freeze out, or overheat anymore.
Be advised of this. This solution is ONLY suitable if you use the remote thermostat, because if you use the hand held remote, the fan will shut off when the room reached the set temp, but that stops all circulation rendering the internal thermostat almost useless.1 -
This sounds like a hack but it is a legitimate setting. Glad you found the solution. Some models let you set a parameter to shut the fan off when satisfied.rick25s said:Problem Solved
The MHK2 remote, didn't alone, fix the problem. I looked at the circuit board (and my electronics technology textbooks from college in 1988) and researched all the labels on the board. I found that there are a couple resisters that double as jumpers controlling the fan. The ones relevant to my model (MSZ-GL) were the jumpers (resisters) labeled JRRE (cool) and JR01 (heat). I contacted Mitsubishi support and they confirmed I was on the right path. The solution was to clip the jumpers off the board. I did this and everything works perfect. The fan shuts off when the set temp is reached, and the room does not freeze out, or overheat anymore.
Be advised of this. This solution is ONLY suitable if you use the remote thermostat, because if you use the hand held remote, the fan will shut off when the room reached the set temp, but that stops all circulation rendering the internal thermostat almost useless.1 -
So what happens when the board fails and a warranty claim is filed?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements