oil leaking
Ezee_70
Member Posts: 3
Hi, I am a retired hvac in Ohio. I'm in my 70's now and so much has changed. My sons friend was certified thru the US Air Force and installed a heat pump at my sons home about a year ago. he started having trouble with it this summer, not cooling good and sometimes freezing up inside and finally shutting down on low pressure. I checked it out and found a leak at the connection joint on the suction line outside. Also there was oil on the ground where the leak was. I'm wondering if that means that the e-coil and txv may now be damaged and may have to be replaced before i even start. So i know he can not afford to have anyone else to fix it, so. Thanks in advance for any advice or help.
0
Comments
-
-
-
-
-
-
Yes unfortunately the dryer is located down inside the unit. So i went by there today late and put my gauges on it and it was empty so wont have to worry about evacuate or pump down. I basically will have to do a install. Thanks Guys for all the comments and advice. Good to be able to discuss stuff with people that has the knowledge and experience in a field i worked in for more then 25 years. I will post and let you all know how it all turned out. Thanks Again.1
-
Ditto on all that. If you're really out of the loop, Google "triple vac". And any chance you have a low pressure nitrogen regulator?0
-
-
Being a heat pump you probably know that you need a bi-flow filter drier.
Yes, the nitrogen gas flow and flush.
The new equip now runs much higher pressure, oil is very sensitive to moisture. Complicated by the reversing valve of the heat pump having very small pilot tubing passages.0 -
Repaired Unit and working fine. I completely disconnected the unit put it on my truck took it to my shop(garage) it made replacing that filter dryer much more easier. Installed a new Dryer but not where the old was, also replaced the TXV just because, hooked it all back up and did a N2 pressure and found one more leak inside at the suction joint and repaired it. Vacuum hold for about a hour, charged it. When i checked the subcooling it was off by 1degree. It seems to be working great. Thanks again for all your advice and comments0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements