Propane issue causing boiler burner fault?
Anything else helpful you guys can think of? Thanks!
Comments
-
Before the problems, were there any maintenance or service calls completed? If Yes , could the parameters for LP gas be changed? Could air-fuel mixture be changed? Could air intake or flue gas exhaust blockage be a problem?
Lack of maintenance is usually not addressed in the troubleshooting section in the manual. When they write those manuals they are working with new equipment. 6 years is a long time to not clean the "innards" of a heater. Expecially them new fangled thingsEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
When was the heat exchanger last cleaned? The condensate trap and drain line?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Yes, the boiler had always been serviced annually by the same contractor since the first year.EdTheHeaterMan said:Before the problems, were there any maintenance or service calls completed? If Yes , could the parameters for LP gas be changed? Could air-fuel mixture be changed? Could air intake or flue gas exhaust blockage be a problem?
Lack of maintenance is usually not addressed in the troubleshooting section in the manual. When they write those manuals they are working with new equipment. 6 years is a long time to not clean the "innards" of a heater. Expecially them new fangled things
Both Air intake and exhaust pipes have been examined and they are free of blockage.0 -
Last maintenance was done in last NovemberIronman said:When was the heat exchanger last cleaned? The condensate trap and drain line?
0 -
-
Do you have the combustion report from the last maintenance? It should be there.0
-
I didn't ask for those reports, but so far what do you suggest could be the source of issue?
0 -
It appears from the way that parts were replaced by guessing, rather than diagnosing, that whether PROPER maintenance was performed is suspect.sunlight35 said:I didn't ask for those reports, but so far what do you suggest could be the source of issue?
Without being onsite and being able to DIAGNOSE, you're asking us to GUESS, and lack of proper maintenance appears to be the consensus.
We want to help, but we can only give advice commensurate with the info that you provide and so far that only includes the parts that were changed and the fact that someone came out annually to service it. That may eliminate some possibilities, but it's not data from which a diagnosis can be made.
Things such as combustion analysis numbers, static and operating gas pressure, burner gas pressure, flame signal strength, the actual extent of maintenance, some pics of the boiler, its venting, etc, would be helpful. Even more helpful would be pics of the interior showing the heat exchanger and burner. Of course, that requires opening up the boiler.
Right now, your description is like someone calling an auto mechanical and saying "my car won't start. I've put gas in it, replaced the battery, alternator, and changed the oil. What do you think is wrong."
You can have the LP company replace the regulator(s), and that may fix the problem or you can get a technician that has the tools and knowledge of how to diagnose. That person can often be hard to find.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.5 -
Thank you Ironman, I understand your reasoning.
What's the chance of having too much methanol in propane would cause burner issue? I am going to ask the propane company see if they can check the gas quality.0 -
That's something you need to ask your LP supplier, but I've never seen it happen around here.
You seem to be fixated on the gas supply being the problem because you state "there are very few other options", but until a proper evaluation and diagnosis of the boiler is done, I cannot agree with that conclusion though it is a possibility.
Deductive reasoning is part of the diagnostic process, but it must be based upon facts (actual readings, measurements, observations), not assumptions.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.4 -
I recorded a video of the start-up:
https://www.youtube.com/watch?v=LTqt_xNjvi0
See if it offers any clue from the sound that it made.0 -
That doesn't really offer much other than it showed 73* outside temp. If that's correct, th boiler would be in WWSD.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
There is a call from DHW0
-
Did this problem occur in days when the temperatures were near 0 degrees. some times when you have a long run of pipe from the propane tank the propane stays in a liquid state and does not become a gas.
I had a friend that ran into this problem, the cure was to put a ten gallon tank in the house to collect the liquid and allow it evaporate and become gaseous. The outlet tap was from the top of the tank the inlet also was at the top of the tank with a syphon tube to have the liquid deposited to the bottom of tank.
Never had the problem again.
Jake
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
-
We had a mild winter this year so this problem happened when temperatures were mostly above 32Fdopey27177 said:Did this problem occur in days when the temperatures were near 0 degrees.
0 -
That burner light-off sounds very lean.
You need combustion numbers, on a clean heat exchanger to go any further!
Excessive methanol in LP cab make the burner wistle and has a bit of a funny smell from the combustion.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements