Ductwrap For Attic AC?
Quick question here regarding ductwrap for a standard cooling only attic system with sheetmetal supply plenum and flex runs in upstate NY.
At the shop I install for we have always wrapped our air handler plenums with SOFT-R fiberglass duct wrap. I have seen the "Reflectix" or "bubble wrap" insulation and this looks to be a much more aesthetically appealing and looks to be easier to work with. However I have heard different things regarding the "Reflectix" insulation such as the R value is lower than SOFT-R duct wrap and you need a barrier of layers to use "Reflectix". I have also heard that "Reflectix" does not insulate well enough and the plenum would sweat if Reflectix only is used to insulate duct work.
Another alternative I have considered is having the sheet metal shop we use to create our plenums "pre insulate" the inside of the plenum. However my question is will the ATD (takeoff) sweat when it is cut into the plenum?
Thank you anyone who has info regarding my questions any help would be greatly appreciated. Just looking for better way come this summer!
Comments
-
The bubble stuff, if it has no reflective layer, is only as good as any other insulation of the same thickness. Which is to say, not very. The reflective stuff is OK if you have a fairly high temperature source which you are trying to insulate from a low temperature sink, as it only affects radiant heat energy. For duct wrap for air conditioning? No...
On sweating. It's all about dew point and surface temperature. If the surface temperature of the metal is below the dew point, it will sweat. Insulation on the outside -- your duct wrap -- will prevent humid air from reaching the cold metal. Insulation on the inside will allow the metal to be as warm as outside. Take your pick. If the takeoffs are uninsulated, chances are they will sweat.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You need to study the PSYCHROMETRICS CHART to understand what's going on.
0 -
Mask all joints.
Mask/air seal all openings between boots, plenum and sheetrock or finished ceilings, walls, and floors. Especially returns. No attic air should be pulled into the system.
R8 fiberglass scrim insulation.
Never use an internal liner. Its nothing but a disease breeding ground.0 -
> @Jamie Hall said:
> The bubble stuff, if it has no reflective layer, is only as good as any other insulation of the same thickness. Which is to say, not very. The reflective stuff is OK if you have a fairly high temperature source which you are trying to insulate from a low temperature sink, as it only affects radiant heat energy. For duct wrap for air conditioning? No...
>
> On sweating. It's all about dew point and surface temperature. If the surface temperature of the metal is below the dew point, it will sweat. Insulation on the outside -- your duct wrap -- will prevent humid air from reaching the cold metal. Insulation on the inside will allow the metal to be as warm as outside. Take your pick. If the takeoffs are uninsulated, chances are they will sweat.
I've had a section of my return that I still need to insulate sweat in the attic. Guess the dew point got to 68-70 up there. I know because of the water stains under it on the flooring.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Jamie Hall said:
The bubble stuff, if it has no reflective layer, is only as good as any other insulation of the same thickness. Which is to say, not very. The reflective stuff is OK if you have a fairly high temperature source which you are trying to insulate from a low temperature sink, as it only affects radiant heat energy. For duct wrap for air conditioning? No...
On sweating. It's all about dew point and surface temperature. If the surface temperature of the metal is below the dew point, it will sweat. Insulation on the outside -- your duct wrap -- will prevent humid air from reaching the cold metal. Insulation on the inside will allow the metal to be as warm as outside. Take your pick. If the takeoffs are uninsulated, chances are they will sweat.HVACNUT said:Mask all joints.
Mask/air seal all openings between boots, plenum and sheetrock or finished ceilings, walls, and floors. Especially returns. No attic air should be pulled into the system.
R8 fiberglass scrim insulation.
Never use an internal liner. Its nothing but a disease breeding ground.
Thank you guys for providing actual useful and real world applicable responses (not just a psychometrics chart). For now I will continue to use R8 SOFTR for attic AC installations. Thanks again to everyone for a great community where I can continue to educate myself in the trade of Heating/ACChrisJ said:> @Jamie Hall said:
> The bubble stuff, if it has no reflective layer, is only as good as any other insulation of the same thickness. Which is to say, not very. The reflective stuff is OK if you have a fairly high temperature source which you are trying to insulate from a low temperature sink, as it only affects radiant heat energy. For duct wrap for air conditioning? No...
>
> On sweating. It's all about dew point and surface temperature. If the surface temperature of the metal is below the dew point, it will sweat. Insulation on the outside -- your duct wrap -- will prevent humid air from reaching the cold metal. Insulation on the inside will allow the metal to be as warm as outside. Take your pick. If the takeoffs are uninsulated, chances are they will sweat.
I've had a section of my return that I still need to insulate sweat in the attic. Guess the dew point got to 68-70 up there. I know because of the water stains under it on the flooring.0 -
R8 May be fine also it may not. That's the reason I posted the chart. You need to calculate the Dew Point of the surface of the insulation to determine if its thick enough to prevent condensation from forming.
Everyone uses 3/8" wall thickness on the suction lines . How many times have you felt the insulation and its wet? Not thick enough to prevent condensation from forming. 1/2' or more may be needed.
0 -
R8 was the thickest I could find anywhere for ductwork.pecmsg said:R8 May be fine also it may not. That's the reason I posted the chart. You need to calculate the Dew Point of the surface of the insulation to determine if its thick enough to prevent condensation from forming.
Everyone uses 3/8" wall thickness on the suction lines . How many times have you felt the insulation and its wet? Not thick enough to prevent condensation from forming. 1/2' or more may be needed.
I used 1/2" on my liquid line and 3/4" on the suction line but it sure did make for a huge lineset. I think it's almost 2.5" in diameter for the suction line.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks again. Agree R8 is the highest I have seen also.ChrisJ said:
R8 was the thickest I could find anywhere for ductwork.pecmsg said:R8 May be fine also it may not. That's the reason I posted the chart. You need to calculate the Dew Point of the surface of the insulation to determine if its thick enough to prevent condensation from forming.
Everyone uses 3/8" wall thickness on the suction lines . How many times have you felt the insulation and its wet? Not thick enough to prevent condensation from forming. 1/2' or more may be needed.
I used 1/2" on my liquid line and 3/4" on the suction line but it sure did make for a huge lineset. I think it's almost 2.5" in diameter for the suction line.0 -
Remember that when wrapping duct to add the thickness of the insulation to your duct dimension to ensure that you are not compressing the insulation compressing the insulation lessen the rates r value , for closure I was taught to cut the insulation off of the wrap to have a proper over lap for agog vapor seal and enough to staple it closed . It should be stapled w the proper stainless staples and proper staple gun outward turning. It should be then have seams tapped w at least 4 inch wide scrim coil tape ,not done yet it should then be bail wired w the wire not being pulled tight. I prefer to hang duct so I add foam tape to my 18 ga strap . If stuck running on attic ceiling rafter I ll get some 2 insulation blue board and sit the duct on that less compression over all . Any time I go to the sheet metal supply house I see that bubble wrap flying out the door it’s garbage , I don’t even know if it goes much . I ve been using 1/2 wall on residential for ac for 20 years to me again any less is garbage the difference in price is a non issue bigger system in commercial spaces and different application are another story . Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements