Will the Takagi T-H3M-DV-N run radiant heat and hotwater
Comments
-
-
Thanks Jamie. I'm trying to find a tankless that will work. My son's that I did is on a gas boiler tankless but the boiler runs to maintain 160 degs. and it's not needed all the time especially spring and fall. any suggestions.0
-
-
I was going to use a heat exchanger to separate the heating from domestic.Not a good idea?
0 -
question, if I were to just use an instant hot for the radiant without using it for domestic hot water will it work?0
-
-
> @zmann96 said:
> question, if I were to just use an instant hot for the radiant without using it for domestic hot water will it work?
@Jamie Hall said it best. It will function but not as well as and for as long as a properly installed and sized boiler.1 -
A tankless water heater is designed to heat small quantities of water 3- 5 gpm over a wide temperature difference say 40- 120F
Boilers are designed with a completely different task, high flow rates, low temperature differential.
As such the internal design, control, etc is quite different.
With so many great choices for the right product why try and force a tankless to do something it is not designed, or comfortable doing?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Thanks Hot Rod. I understand. Well I do Have a 50 gal Natural Gas 50 gal. State Water heater GS6-50-YBVIS 200 45 GPH. It's power vented and is somewhat efficient only a year old. Do you think I could with a heat exchanger do both DHW and the radiant?0
-
Yes I like that much better. There used to be several companies that build a complete box to do that had pump, HX control, piping inside.zmann96 said:Thanks Hot Rod. I understand. Well I do Have a 50 gal Natural Gas 50 gal. State Water heater GS6-50-YBVIS 200 45 GPH. It's power vented and is somewhat efficient only a year old. Do you think I could with a heat exchanger do both DHW and the radiant?
What is the BTU of that heater? A high output 65- 75,000 BTU would be ideal.
I suspect on design day you may need 25,000BTU/ hr. for the home.
Any backup options? On the coldest days you don't have a lot of BTU to spare.
Simple enough to build your own
HX, a couple circulators, air purge, exp tank some purge valves
relay box, thermostat
Here is a drawing I modified a bit to show the concept.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Where in NH are you? Im on the Seacoast... perhaps I can assist. kevin
0 -
Hot Rod, the hot water heater only produces 40K BTUshot_rod said:
Yes I like that much better. There used to be several companies that build a complete box to do that had pump, HX control, piping inside.zmann96 said:Thanks Hot Rod. I understand. Well I do Have a 50 gal Natural Gas 50 gal. State Water heater GS6-50-YBVIS 200 45 GPH. It's power vented and is somewhat efficient only a year old. Do you think I could with a heat exchanger do both DHW and the radiant?
What is the BTU of that heater? A high output 65- 75,000 BTU would be ideal.
I suspect on design day you may need 25,000BTU/ hr. for the home.
Any backup options? On the coldest days you don't have a lot of BTU to spare.
Simple enough to build your own
HX, a couple circulators, air purge, exp tank some purge valves
relay box, thermostat
Here is a drawing I modified a bit to show the concept.0 -
zmann96 said:
Hot Rod, the hot water heater only produces 40K BTUshot_rod said:
Yes I like that much better. There used to be several companies that build a complete box to do that had pump, HX control, piping inside.zmann96 said:Thanks Hot Rod. I understand. Well I do Have a 50 gal Natural Gas 50 gal. State Water heater GS6-50-YBVIS 200 45 GPH. It's power vented and is somewhat efficient only a year old. Do you think I could with a heat exchanger do both DHW and the radiant?
What is the BTU of that heater? A high output 65- 75,000 BTU would be ideal.
I suspect on design day you may need 25,000BTU/ hr. for the home.
Any backup options? On the coldest days you don't have a lot of BTU to spare.
Simple enough to build your own
HX, a couple circulators, air purge, exp tank some purge valves
relay box, thermostat
Here is a drawing I modified a bit to show the concept.
Input BTU rating?
If so, X 78% efficiency= 31,000 actual output. sorry!
Room to add another gas HW tank? That is the least expensive option for those low load jobs.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Yes, I have plenty of room for another tank. do you hook the two tanks together at the heat exchanger for the loop for the radiant heat. Thanks againhot_rod said:zmann96 said:
Hot Rod, the hot water heater only produces 40K BTUshot_rod said:
Yes I like that much better. There used to be several companies that build a complete box to do that had pump, HX control, piping inside.zmann96 said:Thanks Hot Rod. I understand. Well I do Have a 50 gal Natural Gas 50 gal. State Water heater GS6-50-YBVIS 200 45 GPH. It's power vented and is somewhat efficient only a year old. Do you think I could with a heat exchanger do both DHW and the radiant?
What is the BTU of that heater? A high output 65- 75,000 BTU would be ideal.
I suspect on design day you may need 25,000BTU/ hr. for the home.
Any backup options? On the coldest days you don't have a lot of BTU to spare.
Simple enough to build your own
HX, a couple circulators, air purge, exp tank some purge valves
relay box, thermostat
Here is a drawing I modified a bit to show the concept.
Input BTU rating?
If so, X 78% efficiency= 31,000 actual output. sorry!
Room to add another gas HW tank? That is the least expensive option for those low load jobs.0 -
One tank dedicated to DHW, the other just for the radiant.
Tank type water heaters can be a nice heat source as their volume makes for a nice buffer.
Since most do not have an ASME certification no all contractors can or will install them. Check with local code officials.
At 12- 15 psi operating condition they are plenty safe in my mind. Leave all the safeties in place, like the T&P valve, add an additional 30 psi relief if you want low pressure protection.
I would also run it 120- 130° and use a mix valve if you need lower temperature to help prevent extended condensation in the tanks. Tanks set at 100F do not tend to last long without problems,
I have used both gas and electric water heaters from 2-1/2 gallon up to 50 gallon for radiant heat sources.
Bradford White builds a CombCor 2 which is a high output tank water heater with a coil inside for radiant. So an approved dual use tank. I believe they are special order only, now. They were commonly found on some wholesalers shelves, years back.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I was looking at the Combi boilers. Lowes has a Rinnai M120CN 95% and 4.2 gpm. DHW. it's selling for $2658. I can get a 20% employee discount from a family member. Liberty Utilities will give me a $1500 rebate and Uncle Sam will give a $150 tax credit costing me in the end $476.00 I don't want to base the heating system on my savings along. I want it to be efficient and do the job as well. The boiler has a 12 warranty 2 years parts. your thoughts?hot_rod said:One tank dedicated to DHW, the other just for the radiant.
Tank type water heaters can be a nice heat source as their volume makes for a nice buffer.
Since most do not have an ASME certification no all contractors can or will install them. Check with local code officials.
At 12- 15 psi operating condition they are plenty safe in my mind. Leave all the safeties in place, like the T&P valve, add an additional 30 psi relief if you want low pressure protection.
I would also run it 120- 130° and use a mix valve if you need lower temperature to help prevent extended condensation in the tanks. Tanks set at 100F do not tend to last long without problems,
I have used both gas and electric water heaters from 2-1/2 gallon up to 50 gallon for radiant heat sources.
Bradford White builds a CombCor 2 which is a high output tank water heater with a coil inside for radiant. So an approved dual use tank. I believe they are special order only, now. They were commonly found on some wholesalers shelves, years back.0 -
I have not installed that brand personally. What I have found is most every brand and model of boiler you can find rave reviews and terrible reviews.
I stick with brands that support me from the dealer, rep, and manufacturer.
Look for the control features. I thing ramp delay or derate function is important, I like being able to add sensors, outdoor reset sensor should be included.
Read the I&O manual for setup before you buy, are you able to understand the programming, some are super simple, others I've found super complicated.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
well, as I looked into the rebates , it requires a license to apply for rebate. I've installed boilers and hot waters and radiant heat but don't have my license. Even if I paid to have a licensed plumber check my work and sign for me what I pay him would defeat the rebate. I think your advice of a hot water heater makes the most sense for me. I was looking at the westinghouse hybrid . do you know what the flow rate is for it. It only has 130gpm for the first hr. nothing for continuous. There are so many options it's confusing. You are so right about reviews...crazy. I was thinking of the 50k - 100k unit ? for DHW and radiant.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements