Aquastat

I recently removed my domestic hot water from my New Yorker boiler and added a direct vent hot water tank. Do I have to change anything on the aqua stat?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,668
    Is this a steam or hot water boiler? If it is steam, you don't need the aquastat any more, but exactly how you take it out of the control system depends on how it's wired. If it's wired in parallel with the thermostat which otherwise controls the boiler, you can just disconnect it. If it's hot water, it may or may not be the only aquastat controlling the boiler, and what you do with it depends on whether it is or not.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • MSDurica
    MSDurica Member Posts: 8





  • MSDurica
    MSDurica Member Posts: 8
    Thanks, I believe it is the only Aquastat.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited March 2020
    You should replace the aquastat with a modern one like a Hydrostat, and turn off domestic (low limit).
    Now that you have a cold start boiler, you'll want to protect the boiler from low temperature return water.
    You'll now be able to use circulator hold off, and changing the well will also allow you to enable a low water cut-off-to protect the boiler from dry firing.
    Also, unless your power is off, your primary control isn't wired correctly.

    There was an error rendering this rich post.

    HVACNUTSuperTechMSDurica
  • HVACNUT
    HVACNUT Member Posts: 6,266
    It looks like an oil to gas conversion.

    Agree with @STEVEusaPA . Look at the Hydrostat 3250 Plus.

    For a steel boiler, that's not half bad. Horizontal tube, 3 pass, wet leg.
    I'm not positive but I think New Yorker is an offspring of U.S. Boiler. And U.S. Boiler doesn't like conversion burners in their oil boilers for some reason. Lawyer stuff I guess. If that means anything to you.

    Can I ask why you opted for a direct fired water heater vs. an indirect?
    mattmia2MSDurica
  • mattmia2
    mattmia2 Member Posts: 10,799
    edited March 2020
    HVACNUT said:

    Can I ask why you opted for a direct fired water heater vs. an indirect?

    Also my question.

    Might want to cap the tankless so if the coil ever fails it doesn't flood the basement.

    EDIT:
    Don't plug the ports unless you plug them with a relief valve. It is a sealed, heated vessel, it needs a relief to keep it from overpressurizing if the burner control fails to shut off.
    MSDurica
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,341
    @MSDurica

    You cannot disconnect the low limit aqustat it is built into the control. You can replace it with a modern aqustat or set the low limit to it's lowest setting

    MSDuricaEdTheHeaterMan
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    mattmia2 said:


    ...Might want to cap the tankless so if the coil ever fails it doesn't flood the basement.

    Not allowed per code.


    ...set the low limit to it's lowest setting

    Only if the boiler is piped to protect it from low temperature return water.

    There was an error rendering this rich post.

    mattmia2MSDurica
  • MSDurica
    MSDurica Member Posts: 8
    I went with the direct vent water heater due to budget.
  • MSDurica
    MSDurica Member Posts: 8
    Also plunged the ports.
  • MSDurica
    MSDurica Member Posts: 8
    Are there any instruction on how to go from an aqua stat to a Hydrostat
  • HVACNUT
    HVACNUT Member Posts: 6,266
    edited March 2020
    > @MSDurica said:
    > I went with the direct vent water heater due to budget.

    You don't show the boiler piping but I wouldn't think the total cost of a properly installed indirect would be out of the ballpark. But that's another subject.
    STEVEusaPA
  • HVACNUT
    HVACNUT Member Posts: 6,266
    > @MSDurica said:
    > Also plunged the ports.

    It was posted that plugging the ports is against code.

    But it's done and the coil is still open to the atmosphere from the bull ports anyway. I hope.
    STEVEusaPAmattmia2
  • HVACNUT
    HVACNUT Member Posts: 6,266
    > @MSDurica said:
    > Are there any instruction on how to go from an aqua stat to a Hydrostat

    Yeah. Go back up☝️. I posted the I&O manual.
    STEVEusaPA
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228
    edited March 2020
    Look at the white plastic block on the L8124 aquastat. Remove the blue wire from the upper right spade terminal. This will make the L8124 aquastat a cold start control (equal to the L8148 made by Honeywell with one exception).

    Set the low limit to the lowest setting 120° with a 10° differential. Since the circulator will not operate until the boiler reaches the low limit temperature setting, you will want that as low as possible.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 6,266
    > @EdTheHeaterMan said:
    > Look at the white plastic block on the L8124 aquastat. Remove the blue wire from the upper right spade terminal. This will make the L8124 aquastat a cold start control (equal to the L8148 made by Honeywell with one exception).
    >
    > Set the low limit to the lowest setting 120° with a 10° differential. Since the circulator will not operate until the boiler reaches the low limit temperature setting, you will want that as low as possible.

    Granted it's a steel boiler, but I would still want condensate protection.
  • MSDurica
    MSDurica Member Posts: 8
    HVACNUT - Do I leave the blue wire on to get condensate protection?
  • HVACNUT
    HVACNUT Member Posts: 6,266
    Yes. Leave it. The boiler should maintain a minimum temperature of about 135°.

    That's why the Hydrostat 3250 Plus is a superior control. You can have your cake and eat it too.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228
    the L8124 will do that. If you set the low limit at 140° the circulator will not operate until the boiler reaches 140° and stop when the boiler drops to 130°. This should keep you out of the flue gas condensation range.

    By removing the blue wire, the burner will not operate if there is no call for heat. This will reduce fuel consumption

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    SuperTechMSDurica
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228
    Follow-up:
    Agreed that the HydroStat control would be ideal since the manufacturer uses them on the current model of the same boiler. And certainly, we are not paying for the control so the advice does not cost us anything.

    On the "Less Coil" option of the same boiler, they provided an L8148 control. when the electronic aquastats were introduced at a lower price than the old series 80 controls the replacement was L7248. both these controls have no low limit. if the manufacturer believes the cold start control is ok for the boiler less coil, then @MSDurica should be able to set up the control to be a cold start control.

    Just sayin'

    Here is an excerpt from the I/O manual from New Yorker on an older model FR series boiler:

    3. On WATER BOILERS WITHOUT TANKLESS
    HEATERS equipped with L7248 electronic***
    aquastat controller, set High Limit (HL) at 180°F.
    This temperature can be varied to suit installation
    requirements. L7248 controller has the High Limit
    adjustment range from 180°F to 240°F (82°C to
    116°C). High Limit Differential is fixed at 15°F
    (8°C).
    4. On WATER BOILERS WITH TANKLESS
    HEATERS equipped with L7224 electronic aquastat
    controller, set operating control (low limit [LL])
    at 190°F and high limit (HL) at 210°F. Operating
    control (low limit) setting must be a minimum of
    20°F below high limit setting.
    L7224 controller has the High Limit adjustment
    range from 130°F to 240°F (55°C to 116°C), and
    the Low Limit adjustment range from 110°F to
    220°F (43°C to 104°C). High Limit Differential is
    fixed at 10°F (6°C), and Low Limit Differential has
    adjustment range from 10°F (6°C) to 25°F (14°C).

    *** no low limit on this control

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited March 2020
    Who's disagreeing? Cold start with no protection to prevent condensing is bad. Either has to be done in the piping (best) or with the control. Boiler manufacture may provide a high limit only aquastat, which is fine, but always mention properly piping the boiler to protect from condensing.

    Quoting George (the best in the biz IMHO) from the first thread you mentioned...
    ...Don't disconnect the wires in the control, in a liability matter it could make you responsible, FACT! I've seen lawsuits lost over less than that!...

    This is why I recommended replacement which gives you some important extra features.

    There was an error rendering this rich post.

  • MSDurica
    MSDurica Member Posts: 8
    Edith heater man - do I set it at the lowest temp or 140?
    EdTheHeaterMan
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited March 2020
    MSDurica said:

    Edith heater man - do I set it at the lowest temp or 140?

    Edith heater man LOL Ed's wife?
    Do what I said in my first post, for the reason I mentioned in my last post.

    There was an error rendering this rich post.

    HVACNUT
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228
    edited March 2020
    I would set it at the lowest setting, however several are concerned with condensation of flue gas because of low-temperature return water.

    Your radiators will determine if you should keep the circulator off until the water temperature is at least 140°

    What is your Peerless connected to? Cast Iron standing radiators? Copper tube w/Aluminum fin baseboard? Convectors on a Monoflo Tee system? This will determine how fast the return water reaches 130°. If it gets there quickly (less than 5 minutes) then 120° is my recommendation. If it takes 15 minutes or more then you will experience condensation of flue gases and the boiler might rust thru in 10 Years or so.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,228
    Edith heater man LOL Ed's wife?
    That is my brother's wife Archie Bunker Man

    You Meathead!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?