Aquastat
Comments
-
Is this a steam or hot water boiler? If it is steam, you don't need the aquastat any more, but exactly how you take it out of the control system depends on how it's wired. If it's wired in parallel with the thermostat which otherwise controls the boiler, you can just disconnect it. If it's hot water, it may or may not be the only aquastat controlling the boiler, and what you do with it depends on whether it is or not.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0 -
Thanks, I believe it is the only Aquastat.0
-
You should replace the aquastat with a modern one like a Hydrostat, and turn off domestic (low limit).
Now that you have a cold start boiler, you'll want to protect the boiler from low temperature return water.
You'll now be able to use circulator hold off, and changing the well will also allow you to enable a low water cut-off-to protect the boiler from dry firing.
Also, unless your power is off, your primary control isn't wired correctly.There was an error rendering this rich post.
3 -
It looks like an oil to gas conversion.
Agree with @STEVEusaPA . Look at the Hydrostat 3250 Plus.
For a steel boiler, that's not half bad. Horizontal tube, 3 pass, wet leg.
I'm not positive but I think New Yorker is an offspring of U.S. Boiler. And U.S. Boiler doesn't like conversion burners in their oil boilers for some reason. Lawyer stuff I guess. If that means anything to you.
Can I ask why you opted for a direct fired water heater vs. an indirect?2 -
Also my question.HVACNUT said:Can I ask why you opted for a direct fired water heater vs. an indirect?
Might want to cap the tankless so if the coil ever fails it doesn't flood the basement.
EDIT:
Don't plug the ports unless you plug them with a relief valve. It is a sealed, heated vessel, it needs a relief to keep it from overpressurizing if the burner control fails to shut off.
1 -
@MSDurica
You cannot disconnect the low limit aqustat it is built into the control. You can replace it with a modern aqustat or set the low limit to it's lowest setting
1 -
Not allowed per code.mattmia2 said:
...Might want to cap the tankless so if the coil ever fails it doesn't flood the basement.
Only if the boiler is piped to protect it from low temperature return water.EBEBRATT-Ed said:
...set the low limit to it's lowest setting
There was an error rendering this rich post.
2 -
I went with the direct vent water heater due to budget.
0 -
Also plunged the ports.
0 -
Are there any instruction on how to go from an aqua stat to a Hydrostat0
-
Look at the white plastic block on the L8124 aquastat. Remove the blue wire from the upper right spade terminal. This will make the L8124 aquastat a cold start control (equal to the L8148 made by Honeywell with one exception).
Set the low limit to the lowest setting 120° with a 10° differential. Since the circulator will not operate until the boiler reaches the low limit temperature setting, you will want that as low as possible.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
> @EdTheHeaterMan said:
> Look at the white plastic block on the L8124 aquastat. Remove the blue wire from the upper right spade terminal. This will make the L8124 aquastat a cold start control (equal to the L8148 made by Honeywell with one exception).
>
> Set the low limit to the lowest setting 120° with a 10° differential. Since the circulator will not operate until the boiler reaches the low limit temperature setting, you will want that as low as possible.
Granted it's a steel boiler, but I would still want condensate protection.0 -
HVACNUT - Do I leave the blue wire on to get condensate protection?0
-
Yes. Leave it. The boiler should maintain a minimum temperature of about 135°.
That's why the Hydrostat 3250 Plus is a superior control. You can have your cake and eat it too.0 -
the L8124 will do that. If you set the low limit at 140° the circulator will not operate until the boiler reaches 140° and stop when the boiler drops to 130°. This should keep you out of the flue gas condensation range.
By removing the blue wire, the burner will not operate if there is no call for heat. This will reduce fuel consumption
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Follow-up:
Agreed that the HydroStat control would be ideal since the manufacturer uses them on the current model of the same boiler. And certainly, we are not paying for the control so the advice does not cost us anything.
On the "Less Coil" option of the same boiler, they provided an L8148 control. when the electronic aquastats were introduced at a lower price than the old series 80 controls the replacement was L7248. both these controls have no low limit. if the manufacturer believes the cold start control is ok for the boiler less coil, then @MSDurica should be able to set up the control to be a cold start control.
Just sayin'
Here is an excerpt from the I/O manual from New Yorker on an older model FR series boiler:
3. On WATER BOILERS WITHOUT TANKLESS
HEATERS equipped with L7248 electronic***
aquastat controller, set High Limit (HL) at 180°F.
This temperature can be varied to suit installation
requirements. L7248 controller has the High Limit
adjustment range from 180°F to 240°F (82°C to
116°C). High Limit Differential is fixed at 15°F
(8°C).
4. On WATER BOILERS WITH TANKLESS
HEATERS equipped with L7224 electronic aquastat
controller, set operating control (low limit [LL])
at 190°F and high limit (HL) at 210°F. Operating
control (low limit) setting must be a minimum of
20°F below high limit setting.
L7224 controller has the High Limit adjustment
range from 130°F to 240°F (55°C to 116°C), and
the Low Limit adjustment range from 110°F to
220°F (43°C to 104°C). High Limit Differential is
fixed at 10°F (6°C), and Low Limit Differential has
adjustment range from 10°F (6°C) to 25°F (14°C).
*** no low limit on this controlEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
BTW: this ain't the first time we all disagree on this topic!
https://forum.heatinghelp.com/discussion/84513/bypassing-low-limit-switch-on-honeywell-l8124a-aquastat
and
https://forum.heatinghelp.com/discussion/123384/changeover-to-cold-start-boiler
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Who's disagreeing? Cold start with no protection to prevent condensing is bad. Either has to be done in the piping (best) or with the control. Boiler manufacture may provide a high limit only aquastat, which is fine, but always mention properly piping the boiler to protect from condensing.
Quoting George (the best in the biz IMHO) from the first thread you mentioned...
...Don't disconnect the wires in the control, in a liability matter it could make you responsible, FACT! I've seen lawsuits lost over less than that!...
This is why I recommended replacement which gives you some important extra features.There was an error rendering this rich post.
0 -
-
Edith heater man LOL Ed's wife?MSDurica said:Edith heater man - do I set it at the lowest temp or 140?
Do what I said in my first post, for the reason I mentioned in my last post.
There was an error rendering this rich post.
1 -
I would set it at the lowest setting, however several are concerned with condensation of flue gas because of low-temperature return water.
Your radiators will determine if you should keep the circulator off until the water temperature is at least 140°
What is your Peerless connected to? Cast Iron standing radiators? Copper tube w/Aluminum fin baseboard? Convectors on a Monoflo Tee system? This will determine how fast the return water reaches 130°. If it gets there quickly (less than 5 minutes) then 120° is my recommendation. If it takes 15 minutes or more then you will experience condensation of flue gases and the boiler might rust thru in 10 Years or so.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Edith heater man LOL Ed's wife?
That is my brother's wife Archie Bunker Man
You Meathead!Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements