Using Nest with air handlers
samosa
Member Posts: 2
I have 2 Mitsubishi unit sez kd12na4r1.th each connected to it's own nest thermostat in our house. I am having issue cooling the house down as it constantly stays at 70f during the course of the night. Do I need to play with settings
0
Comments
-
This Mitsubishi unit is not compatible with Nest Learning Thermostats. the indoor and outdoor units communicate with a 2 or 3 wire communication protocol. There should be a Mitsubishi wired remote control that acts as a thermostat on your wall.
Nest thermostat is designed for non communicating systems that use industry-standard wiring that operates relays as follows:
R terminal is for 24v. AC power
C terminal is for 24v. AC common
Y terminal is connected to R on a call for cooling
W terminal is connected to R on a call for heat
G terminal is connected to R on a call for fan operation
The heat pump operation is slightly different. but uses the same principle to connect R terminal to various other terminals or operate reversing valve solenoid and relays for fan and compressor.
I'm interested in how you connected the Nest to the Air handler?!?Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I used Mitsubishi PAC-US444CN-1 along with
RIAD MAGNETICS VPL24-2100 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements