Help with old two pipe direct return system

Options
TonyDestro
TonyDestro Member Posts: 5
edited February 2020 in THE MAIN WALL
I own a 1920s house with what appears to be an old two pipe direct return system. It appears that two radiators were removed from the system (bathroom, kitchen) and the supply and return lines for those radiators capped off. There are five remaining Columbia brand radiators. The balance valves which appear to be the originals on the radiators appear to be seized up. The system seems to work very well, with only a few things to complain about. The upstairs is too hot in the morning. I can't find any type of air separator on the system anywhere. The one radiator makes a banging noise once when the system fires up. There are no unions or valves to isolate the boiler for service. The shutoff valve turns but will not close. The expansion tank is the old kind with no bladder and on the return, on the suction side of the circulator, which is also on the return.

My father was a master plumber with lots of hydronics experience, unfortunately he recently passed away due to leukemia and so cannot help me. He taught me a ton, but almost nothing about hydronics.

What changes would you make to this system if it were yours? Right now I am thinking TRVs, but I am tempted to move the circulator to the supply and install a caleffi discal on the supply and a modern expansion tank, then remove the old expansion tank. The manual for this boiler explicit shows the circulator on the return though.














Comments

  • Steamhead
    Steamhead Member Posts: 16,844
    Options
    Regarding the unbalance, the first thing I'd do is put a radiator in the kitchen.

    I'd also repipe the boiler. At the moment it's getting a lot of cold return water, which can cause flue gases to condense in the chimney or the boiler itself. W-M's piping specs for this type of system are on pages 24-25 of the current manual, here:

    https://www.weil-mclain.com/sites/default/files/field-file/CGi Series 3 Boiler Manual 1016 Web Version - Starting CP7531680.pdf

    Regarding the expansion tank- if you add a proper air separator and pipe it to the tank via an Airtrol tank fitting, it should not waterlog. I much prefer this setup to bladder or diaphragm tanks, since these tend to fail over time. I see a lot of older plain-steel tanks, but never an older bladder/diaphragm tank.

    Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2
  • nicholas bonham-carter
    Options
    If you loosen the packing nuts on the radiator valves, you can often get the handle to turn.—NBC
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    It looks like those valves may be some early version of a ball valve, maybe with the stop missing so they turn 360 degrees but have a definite on and of position.
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Options
    Looks piped correctly to me for a Closed type compression tank (pump on return), per the manual. But you probably should replace that and install a modern expansion tank as mentioned, and switch the pump around to supply side.

    I would add a air scoop Or separator there too to make you life easier The water feed also connects there.
  • pecmsg
    pecmsg Member Posts: 4,861
    Options
    That appears to be an old gravity system. In reality your heating way more water then needed.
  • hot_rod
    hot_rod Member Posts: 22,158
    Options
    If you are up for a major repipe I would do a home run system, 1/2 pex to each radiator with TRV added. it would be nice to get rid of all that steel piping :)

    First step would be a room by room heat load calculation. confirm that radiators are adequate in each room.

    No sense in adding components until you have a load calc.


    https://www.slantfin.com/slantfin-heat-loss-calculator/
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • SuperTech
    SuperTech Member Posts: 2,166
    Options
    @hot_rod Wouldn't it be a good thing for him to keep the oversized piping in case of the possibility of a future mod-con replacement boiler? I could be wrong but I thought I remember hearing that condensing boilers work well with high mass.
    Personally I would keep the existing boiler and do a nice home run manifold setup like you suggested.
  • hot_rod
    hot_rod Member Posts: 22,158
    Options
    The piping mass and content would act as some buffer no doubt. But uninsulated piping, where you may not need or want the heat. A buffer with a mind of its own. I'd rather buffer in a well insulated tank if a buffer is actually needed after a rebuild.

    A load calc, properly size a modulating boiler to the load running the lowest SWT. With the smallest boiler, turndown, ramp delay, heat derate feature, ODR , etc that is about as good as it gets nowadays. Light years ahead of what is going on now.

    And always the load calc is the only road map to a successful system.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • TonyDestro
    TonyDestro Member Posts: 5
    edited February 2020
    Options
    All of your comments have been extremely helpful.

    I'm worried if I loosen the packing I will have to replace the packing. I'll just get those materials. It might be easier to just replace the packing instead of spud wrench and replace?

    Some comments: The piping is the only thing keeping the basement remotely heated. I'm not sure the home run system would be all that much work, really. I have pex tools. Except for lugging all that old pipe out.

    My dad told me it was possible to add a rads in the basement (there is a bathroom on this level that is again only poorly heated by the large piping) He also said I could add a radiator in the garage (which sits lower than the basement, is about 10 feet from the house, and under ground. He said to use his Hydro Drill and bore a hole through the wall directly into the garage or to contact a plumber who owns a directional drill.

    I'm going to do my homework on the heat load calc.