Combustion analyzer with digital I/O port.
jlag
Member Posts: 9
Do any manufacturers make a reasonably priced (< $1K) combustion analyzer for #2 residential with a digital IO port (usb, serial, wifi, Bluetooth, etc.)?. I wish to use this for a boiler monitoring system I am working on in order to start analysis and send results to a data acquisition system.
Bacharach Intech allows you to download data into you I-phone but only one at a time. Not sure how long you are conducting the test? To datalog for more than 15-20 minutes would take special sensors and sampling assemblies.
CO2 varies based on the current btu content of the fuel. CO2 readings can be misleading. All fuels produce close to 100% of their CO2 value, whatever it is. O2 determines how much it is diluted, O2 is always 20.9%. Analyzers that calculate CO2 use 11.7% or 11.8% as there guideline, but this does not apply to the actual btus of the fuel.0 -
I don't know of any analyzers that measure CO2. Most if not all measure O2 and CO then calc the CO2. I really don't understand why boiler manufactures specify CO2 readings, no one is actually taking them.ratio said:
WHy not? Don't some combustion analyzers use CO2 instead of O2?B_Sloane said:NEVER use C02
Albert Einstein1 -
Huh. I thought most used one type of sensor & a few used the other.0