Slant Fin Heat Loss Calculation App
mferrer
mferrer Member Posts: 40
As an Instructor in Hydronic Heating, I stress the importance of heat loss calculations for sizing HW boilers. I've played around with the Slant Fin phone app and found it fairly easy to use although I haven't actually used it for a specific job as I am not a contractor.
I was wondering if any companies here have used it. Is it a reasonable heat loss calculation tool? I would only recommend it to young students for educational purposes, but would be interested if it is widely used. It is a free app. What other tools are commonly used?
Thank you all!
  • Leon82
    Leon82 Member Posts: 681
    It usually comes in a little higher than the manual j or fuel use survey. It was about 10000 btu higher than my field use calculation
  • Zman
    Zman Member Posts: 7,609
    The Slant Fin app is user friendly and reasonably accurate. It should work well for your application.
    For residential projects I usually use the one in Siggy's Hydronic Design Studio. I built a spreadsheet version that works well for unusual or very large buildings.
    Albert Einstein
  • GroundUp
    GroundUp Member Posts: 2,513
    I think the Slant Fin app sucks. It's awful to navigate, and always 20-30% high. There is an online calculator at builditsolar.com that is right on the nose with manual J and is super easy to use, and obviously much more accurate.
    EBEBRATT-Ed Member Posts: 20,194
    I like Slant Fin, it is simplified but most don't want to take the time to do any heat loss so it's better than a guess that's for sure.
    Some say is comes in high in my experience it is conservative but not what I would consider high.
    Like any calculation if you don't put the right numbers in the result will be wrong
    Other tool ? The B & G "System Syzer" you can get the wheel or uses it electronically
    Jamie Hall Member Posts: 27,379
    For what it's worth, I have used the Slant/Fin app several times, and on several rather odd applications. So far it has proven to be remarkably close to reality, The one thing I would say about it is that it is deceptively simple, and this can be a problem. If one doesn't pay attention to the numbers one is putting in and the assumptions which they are based on, it can be off. But then, so can any other calculation.
  • mferrer
    Thank you all! I appreciate the comments. I will look into the other apps mentioned. Thanks for reminding me about the B & G System Syzer. I know I have one of the wheels somewhere. Just have to find it.
    Thanks again!