"Flooded" radiator
BrotherMax
Member Posts: 6
I'm Brother Max, a Franciscan religious brother in the South Bronx. We've got One-pipe steam, in what used to be a convent, 5 floors. A radiator on the 2nd floor spurts water from the air vent, even a brand new one. It doesn't happen elsewhere in the building. I know I've got wet steam, but the other radiators seem ok. Ideas? Thanks.
0
Comments
-
Hi Brother Max!
What is the size of the vent? A slower one might do better (if the water is due to extra-fast condensation in the cold radiator).
Is the radiator sloped toward the pipe side? Check with a level across the top. Proper slope will keep extra condensate from collecting in the radiator.
What is the pressure setting on your boiler?
You said "spurts". Do you mean like a steady stream of spraying water, or do you mean some dribbling/dripping?
How do you know you have wet steam? Can that be improved? Maybe we can help you improve it.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
In addition to @ethicalpaul 's comments, check the pipes leading to that one radiator. It's possible that a length of what should be a pipe gently sloping away from the radiator has shifted to slope to the radiator -- another place to trap condensate and have it spurt out of the vent. Although that arrangement will usually have a water hammer associated with it, not always...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
The condensate is not draining from the radiator.
1. Check to see if the radiator shut off valve is fully open.
2. check to see if the radiator pitched in the right direction. The back of the radiator must be slightly higher than the steam inlet side.
3. Wet steam is not an issue in radiators as steam becomes water when the energy BTUs are used up.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements