Single-pipe steam heat for very small room

orick
orick Member Posts: 7
edited December 2019 in Strictly Steam
My 1870s house has single-pipe steam running off of a Weil-McLane boiler. I've been really happy with the steam heat (quiet, consistent, and no air blowing around).

My house has a very small bathroom underneath the stairs leading to the second floor. There is no heat source for the bathroom, and it gets very cold in the winter because it's on an exterior wall.

What's my best option for heating this bathroom?

There are steam pipes in the cellar within a few feet of the bathroom, so it would be easy to run a steam pipe through the floor. But even the smallest cast iron radiator (that I've found, anyways) would be too big for this bathroom, both in terms of fit and in terms of heat output.

If I just want to add a little bit of heat, can I just run a black iron pipe through the floor and cap it? Would that be pointless? Is there some kind of tiny radiator I could install?

Thanks for any ideas.

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,383
    edited December 2019
    There are small ones that go inside the wall and there are also wall mounted ones.

    Are you sure the smallest you found won't fit? They make them pretty small! And are you sure it wouldn't provide enough heat? They put out a good amount of heat for a tiny room.

    You can do the pipe, but don't cap it. Instead put a radiator vent on the top of it. This is not unheard of but it would provide less heat than any radiator I think.

    You could run the pipe up to a strong shelf with a small radiator on it although a lot of the heat would go up and not warm your feet.

    You could also do a radiant loop off of your steam boiler.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • orick
    orick Member Posts: 7
    Thanks for your reply!


    Are you sure the smallest you found won't fit? They make them pretty small! And are you sure it wouldn't provide enough heat? They put out a good amount of heat for a tiny room.

    The smallest I found I think would put out too much heat. E.g., the Burnham slenderized 4X19X4, which is rated for 1,536 BTU with steam. The room is only about 20 sf with a low ceiling.

    I have not seen any very small wall steam radiators. If you have any in mind, please point me in the right direction.

    You can do the pipe, but don't cap it. Instead put a radiator vent on the top of it. This is not unheard of but it would provide less heat than any radiator I think.

    This is along the lines of what I was thinking. I'm just wondering if the heat output would be enough to make a difference (I don't need it toasty, but taking the edge off the cold would be good).

    You could also do a radiant loop off of your steam boiler.

    A hot water loop is probably a good solution, but I am hoping to find a more economical option.
  • Jamie Hall
    Jamie Hall Member Posts: 24,493
    You can check to see if the pipe idea would work. Pipes have an EDR, too, just like radiators! It's the surface area of the pipe -- so take the circumference, multiply times pi -- 3.14 -- divide by 12 to get feet, and multiply by the length of pipe in feet. That will be the EDR. Say you have a pipe with a 2 inch diameter. That would be about 2 square feet for a 7 foot tall pipe. 500 BTUh? Might be enough. What's the exterior wall area?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 6,383
    Ahh OK I misread your original post regarding your concern about the heat output. You can always cover some or all of it with something to limit the heat. That 4x19x4 is very small, I have one like it.

    here is the in-wall kind. I pulled one very much like this out of my bathroom prior to installing a new radiant floor: https://images.app.goo.gl/ZRd5r3znrnpuwfyg7

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • orick
    orick Member Posts: 7

    What's the exterior wall area?

    The exterior wall area is about 32 sf. Very helpful math, thank you!
  • orick
    orick Member Posts: 7

    Ahh OK I misread your original post regarding your concern about the heat output. You can always cover some or all of it with something to limit the heat. That 4x19x4 is very small, I have one like it.

    here is the in-wall kind. I pulled one very much like this out of my bathroom prior to installing a new radiant floor: https://images.app.goo.gl/ZRd5r3znrnpuwfyg7

    You got me thinking about putting a little radiator behind the toilet, in the unused space beneath the first few steps (a good solution, but lots of work). The photo below is not my house, but gives you an idea of the layout. (The sink is inside the door to the left. If I run a pipe through the floor, the easiest place to bring it up would be under the sink.)


  • ethicalpaul
    ethicalpaul Member Posts: 6,383
    Yeah, that would be good. Maybe under the sink too if you have or can get a small attached-to-the-wall kind

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Jamie Hall
    Jamie Hall Member Posts: 24,493
    32 square feet? No windows? If we are a bit pessimistic and assume an R value of 4 for that, then you're looking for 8 BTUh per degree of difference between inside and outside. If your outside design is 0 and you want the occupants cosy, say at 70 -- then you really only need around 600 BTUh max...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • KC_Jones
    KC_Jones Member Posts: 5,792
    This was a custom solution by one of the pros on this site. Post 5 in this thread.

    https://forum.heatinghelp.com/discussion/151994/new-steam-mini-tube-installation-in-ohio/p1

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Steamhead
    Steamhead Member Posts: 17,312
    orick said:

    You got me thinking about putting a little radiator behind the toilet, in the unused space beneath the first few steps (a good solution, but lots of work).

    You don't want to put the radiator behind the toilet.

    Remember the sign that says "We aim to please- you aim too, please"?

    Not everyone does :#
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Hap_Hazzard
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    If you can find an old junk radiator you can remove everything except the first and last section an end up with a tall, narrow radiator that would fit in any corner. Don't even bother with a valve; just stick a street elbow in the supply end and run a riser into it.

    If you can't find a used one, Castrads makes an 18" 2-column, 4-section radiator that's only 4 EDR.

    https://www.castrads.com/us/product/mercury-2-column-18in-4-sections/
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    edited December 2019
    The trouble with using pipe to heat the space is that steel pipe doesn't hold heat as long as cast iron radiators, so it will still be cold in there between heating cycles.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • Phil53
    Phil53 Member Posts: 73
    I think a 2 Ft. piece of CI baseboard would work well. Just vent and pitch it a little.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    True. It doesn't stick out much and it retains heat well. With the ease of access he could even run separate supply and return lines if he needed to.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • Gsmith
    Gsmith Member Posts: 439
    Cast iron baseboard should work fine, I have it in my one bathroom. Just pitch it well and use a good vent.
  • orick
    orick Member Posts: 7
    Thanks everyone for the ideas.

    If I go with a baseboard, I think I could run a separate return line. Are there good alternatives to the Baseray (or is that a solid option)? https://www.usboiler.net/product/baseray-baseboard-radiator.html

    If you can find an old junk radiator you can remove everything except the first and last section an end up with a tall, narrow radiator that would fit in any corner. Don't even bother with a valve; just stick a street elbow in the supply end and run a riser into it.

    I did not realize that was a possibility. Will the sections really come apart? Aren't they welded together? How would I attach the first/last sections together?


    If you can't find a used one, Castrads makes an 18" 2-column, 4-section radiator that's only 4 EDR.

    https://www.castrads.com/us/product/mercury-2-column-18in-4-sections/

    Thanks--that would be really nice, but blows up my budget. It looks like there are lots of good options for economical small two-column radiators in the U.K., but not so much here in the U.S.

  • orick
    orick Member Posts: 7
    orick said:

    I did not realize that was a possibility. Will the sections really come apart? Aren't they welded together? How would I attach the first/last sections together?

    Looks like others have been down this road before.

    https://www.youtube.com/watch?v=6rPADasYq70

    This could be a really neat project. But after it all I would probably wish I just bought the smallest Burnham slenderized and installed it with a stingy vent.

  • coelcanth
    coelcanth Member Posts: 89
    i think you would be very comfortable with a 2" black iron pipe riser-radiator because my 1920's house has this exact arrangement in its two bathrooms.

    the steam supply runout under the floor is smaller, but the simple 2" pipe in the corner runs almost the full 9 feet of the bathroom with a cap just below the ceiling. side of the pipe is tapped for a regular 1/8" angle air vent. i use a Hoffman 40.
  • JUGHNE
    JUGHNE Member Posts: 11,248
    Have you considered a small electric heater?
    A wall mounted cove heater is up and out of the way.
    Wall tstat is recommended versus unit mounted type.


    I have a 1/2 bath, 5X5, fortunately no exterior walls. It has a 4 bulb wall light. 240 watts heat it well. I turn the lights on a few minutes before a comfortable reading session......
  • orick
    orick Member Posts: 7
    coelcanth said:

    i think you would be very comfortable with a 2" black iron pipe riser-radiator because my 1920's house has this exact arrangement in its two bathrooms.

    the steam supply runout under the floor is smaller, but the simple 2" pipe in the corner runs almost the full 9 feet of the bathroom with a cap just below the ceiling. side of the pipe is tapped for a regular 1/8" angle air vent. i use a Hoffman 40.

    Thank you! I am seriously considering this, especially in light of your endorsement.
    ethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,251
    @orick I think the 2" pipe would be fine. If you need more heat than that you could use a piece of steel fin tube mounted vertically and build an enclosure around it with expanded metal and wood (like a radiator enclosure).

    As I recall @gerry gill made a welded radiator if you search his posts
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 363
    Adding another voice to the go ahead with the pipe: grew up in an apartment where the smaller bathroom had a 2 or 2-1/2" pipe with vent (we were on the top floor) for heat with two outside walls and a leaky window and it was mostly fine.