Heat expansion noise

I raised a problem radiator about 1/4" on the supply side and 1/2" on the vent side. I no longer have water hammers but now have knocking sounds coming from the pipes.

Do the joints need time to settle out to the new radiator height? Haven't had this issue before when I raised radiators to correct pitch of either radiators or run outs.

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,383
    Maybe the slope problem or “valley” got moved and you’re hearing water hammer farther down the pipe.

    Or your work increased tension (removed free play) in the pipe and it is expansion noise.

    Is this an upstairs radiator or can you listen/observe in the basement?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 10,702
    In addition to water hammer somewhere new it could be that it is now binding against a hole in the framing and sticking ans slipping as it expands and contracts. Depends on the sound of the "knock".
  • pecmsg
    pecmsg Member Posts: 5,230
    Lower it a1/4” and see what happens.
  • gfrbrookline
    gfrbrookline Member Posts: 753
    @pecmsg that's what I did and it fixed the problem. Good call.
  • gfrbrookline
    gfrbrookline Member Posts: 753
    I know a lot of people here recommend pocket change for shims, I like cedar blocks since they can spread the weight of the radiator foot over three floor boards to reduce sinking on one board.
    SeanBeans
  • BobC
    BobC Member Posts: 5,495
    I used plywood strips about 1-1/2" wide (adjust length to fit radiator depths), they are cheap and can be stained so they don't swear at the floor. You can use different thicknesses to correct slope issues.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge