Ghost Flow? additional spring check valve?
Radiant heat was installed on the main floor and basement coupled on the existing baseboard heating upstairs. This is the second heating season. The issue is up stairs bedroom are getting warm without the thermostat calling. Looking at the piping it has one supply and two return pipes to the manifold. I see already a spring check valve was installed on the supply line to the upstairs baseboard. I think the ghost flow is going up the return and moving around (like a race track) see attach schematic. My question is could I install another spring check valve on the return side?
Thank you again for the help.
Thank you again for the help.
0
Comments
-
Page 12 of this B&G booklet answers your query Start reading in the second column just below the diagram of "ONE ZONE ONE CIRCULATOR" and continue on page 13. Illustrates your "Ghost Flow"
http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdfEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Correction start on Page 11 second column "ONE ZONE ONE CIRCULATOR" and on page 12
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Pics would be better of the whole boiler piping arrangement. Not too close. There could be other factors involved. The existing circulator is not an IFC? Internal Flow Check.0
-
Will do get a picture posted . Thank you for the ONE ZONE ONE CIRCULATOR.
The TACO 007 is not IFC. A spring check valve is installed on the supply line already on both circuits for the base board. The radiant circuits has Grundfos with check valve already. I will work on that picture of the mechanical room.0 -
It would be unusual to require two checks in a system like that.
Sometimes primary secondary piping with two vertical lines piped off the closely spaced tees can "back end" heat. Hotter water rises up the center of the return riser while cooler water falls down the outer portion of the tube, a thermosiphon basically.
A drawing would better help us see what could be the cause.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I have attached power point presentation (watch in slide show) pictures of the mechanical room also made a heating schematic. Slide one shows the red pex return lines with two green handle ball valves and in Slide two has a better picture of the red pex return lines with the green ball valves and going into the copper pipes. Any question please ask. Thank you again0
-
Look at the returning pipes from that split system , they should return to a single pipe before conecting to the return manifold . If not that is the problem ....
There was an error rendering this rich post.
0 -
There's a reason why zone valves are used when one would think that check valves suffice.0
-
Any pics? Nothing beats actually seeing the crime scene for real.0
-
The attachment did not go thru. Sorry please recheck my last discussion0
-
Sorry for the trouble. I convert them to Word docX I hope this works< Also the attachment are in pdf form.
If this does not work please tell me what form and I will get it done.
0 -
Thank you all. I read Edtheheaterman attachment and after watch Caleffi "Heat Migration in Hydronic & Plumbing Systems" Now I understand "ghost flow".
Thank you again for all the support.
You Tube video:
https://www.youtube.com/watch?v=23CQiEt5QWc&list=PLuuV0ELkYb5VE0I4evUZ30b5U78CRlRdg&index=360
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements