Changing wet return layout

samstu
samstu Member Posts: 14
edited November 2019 in Strictly Steam







Hi all,

I’m replacing a section of corroded wet return, and it looks to me like it’s split up in a certain section for no reason. Photos aren’t great so I highlighted the existing wet return in green. In one picture I marked the pipe that looks unnecessary to me in red X’s with the new proposed layout in green.

(One wet return is coming from back of building (at top of picture, and other is coming back from front of building (up from bottom of picture).

I also attached a photo with arrows showing the directions in which I believe the condensate is flowing back to boiler.


Because I’m hesitant to change original (or maybe it wasn’t) layout, I wanted to see if there seems to be an issue with what I’m proposing or if it looks ok.

Thank you!

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,496
    Wet returns are nice. So long as they stay below the water line of the boiler by a few inches, you can run them pretty much anywhere and any way you want to. They can even be run in copper, if you prefer.

    A tip, though: it's very nice to have cleanout Ts or at least hose bibbs at strategic locations, so you can flush them out if and when you want to.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JUGHNE
    JUGHNE Member Posts: 11,248
    Do you have access to the the other ends of the wet returns?

    If so if you could add tees, ball valves and hose bibs.
    With this set up on each end you could flush and test for leaks.
    Maybe just 15 PSI applied would let you know if leakers underground.
  • samstu
    samstu Member Posts: 14
    edited November 2019
    @Jamie Hall does that mean even up and down a couple inches as long as it stays comfortably below the water line? Theoretically it makes sense to me but I seem to recall reading that wet returns should slope slightly down to boiler or at least be level or am I wrong? Thanks for the clean out tip

    @JUGHNE

    I do not it’s buried and hopefully not leaking we’ll see what happens when the water pressure is no longer escaping from the corroded exposed sections. Can you please elaborate on the optimal setup that will allow flushing the returns in the future?
  • Jamie Hall
    Jamie Hall Member Posts: 24,496
    Wet returns can go up and down and sideways all over the place, just so long as they stay below the water line. The suggestion that they should slope to drain is fundamentally good -- but the idea there has nothing to do with running the system, but with making it easier to flush them out if they get gunked up. Which is why I suggest cleanouts where they change direction.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • samstu
    samstu Member Posts: 14
    @Jamie Hall wow thanks that’s great I never realized that. Makes sense.
  • JUGHNE
    JUGHNE Member Posts: 11,248
    IIWM, for flushing I would have a ball valve on each end maybe a foot above the floor, this would isolate the rest of the system from the wet return. Then below that on each end a 3/4" port that would have a hose bib installed. Ideally, with the isolation valves closed, you could take a hose to one end for the pressure flush. Use a double female fitting for the supply hose. Then the other hose bib would drain away to floor drain.

    If you have no access to the other end of the return then place the hose bib low on the end of a tee so that you could isolate that return from the boiler and power surge back and forth to loosen sludge up. Carefull to not push water up to the dry return as this could compound things.

    If you have leaky pipes you see in the dirt? then you might have some leaks under the floor.

    Are you losing a lot of water?
  • samstu
    samstu Member Posts: 14
    edited November 2019
    @JUGHNE Thank you for describing the optimal setup, I appreciate it.

    Yes we had some leaking sections under ground. It started off in one section and once we replaced that section the pressure just moved on to the next weakest part and exited. Now replaced a large length and hoping that it will hold.