My gas meter just quit screaming at me!
old_washer
Member Posts: 4
in Gas Heating
Left - old boiler #39
Middle - new boiler #47 (OEM)
Right - new boiler #51 (after derating for elevation)
This just might help get the NG bill down under $100/mo?
well......depends on how many there were in the old boiler vs new...
Looks like it should help though!0 -
What elevation are you at and how did you calculate the size for that altitude?0
Old Boiler had 7 orificesdelta T said:well......depends on how many there were in the old boiler vs new...
New boiler has 6.
5,500 ft (Suburban Denver)JUGHNE said:What elevation are you at and how did you calculate the size for that altitude?
The boiler came with #47s.
Manual states up to 4500 ft should be #49s.
Derate at 4% per 1,000 ft above 1,000 ft = 16%
Old boiler clocked at nearly 145K
New boiler clocks at ~82K with #51 orifices
What is the boiler rated too? Has a combustion analysis been done?
Denver natural gas is already derated so you often don't need to go as small as you think. Smaller orifice does not necessarily mean higher efficiency. There is a lot more to it."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The derated gas probably makes up for the air density perfectly in your case. If I was guessing, I would think the sea level orifices are pretty close for correct combustion. A combustion analysis will tell you for sure."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@Erin Holohan Haskell, both of the PDFs above didn't download cleanly, the first one ended up named 'NaturalGasDerate.PDF' & the second is named 'Trane --note the single quotes are part of the filename on my PC. Firefox 70.0.1 (64-bit), Windows 10 Pro Version 10.0.17763 Build 17763.0
Thanks for letting us know, @ratio. We've been investigating this issue. If you remove the quotes in the file name, you should be able to open the file. So sorry for the inconvenience.
President
HeatingHelp.com0 -
- 119 Geothermal
- 394 Solar
