HTP VersaHydro Solar whining

jklingeljklingel Posts: 1Member
I have a 4-yr-old HTP VersaHydro Solar propane mod-con boiler, and it has a loud whine in it periodically. The whine started a year or so after installation. A factory tech, myself, and a boiler pro all recently felt the whine indicated a bad blower fan bearing, so I replaced the blower fan. That was 2 weeks ago. All was fine for 3 days, but the whine started again. It only whines when the blower fan is in the range of 27-29% of the max speed. Also, the boiler will sometimes run quietly in that speed range. A week ago I called a factory tech and he said it sounds like another bad blower fan bearing, or a propane pressure problem. A pro is coming Tuesday to measure the pressure in the manifold as a starting point. Has anyone else had a similar whining problem? No one in my town works on these boilers, so any information/experience I can pass along to the pro will be appreciated, even if the same problem has happened to you on a different brand. Thanks in advance, and I hope I made myself clear. Puzzled in Fairbanks.

Comments

  • ZmanZman Posts: 5,262Member
    Someone needs to do a combustion analysis and tune the boiler properly. Simply guessing and adjusting gas pressure will not fix this.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Rich_49Rich_49 Posts: 2,536Member
    Contact HTP . We had a unit that we designed for in Maine that had a few issues . First issue was wet gas (propane) , propane guy addressed that . No fan issues on that one . Issue 2 was the 0-10v control on the on board circ was operating below 4 volts at times in a really tight house which created an issue with noise , we addressed that by changing the programmed Delta from 20* to 10* , sped the circ flow up and issue disappeared .

    HTP has a device they can send you to be hooked up and monitored remotely by engineering at HTP to assist in identifying issues
    You didn't get what you didn't pay for and it will never be what you thought it would .