Honeywell sv9641 lp gas valve NEED HELP
Brad007
Member Posts: 7
I just replaced a Honeywell sv9641 gas valve and converted it to LP I also changed the pilot assembly I am getting error code 6 I have 10.8 in WC on inlet of gas valve. The hot surface igniter lights three times and goes into lockout. I need some advice thank you
0
Comments
-
IIRC, these "Smart" valves have a tiny switch on them. Easy to inadvertently turn off.0
-
The switch is in the on position0
-
Is that valve specifically for LP or did you get HW kit for conversion? Is the pilot for LP?
Could the pilot adjustment screw be set too low ?
You never get any pilot flame, is that right?0 -
I had to covert the new gas valve to lp and the new pilot assembly is the same number as what was there. I adjusted the pilot screw and still had no gas coming through the valve0
-
What exactly are you working on brand, model, pictures help. Some systems will have pressure switches that need to make before gas flow.
D0 -
Tempstar high efficiency furnace model n9mp1075b12b1 and serial A0330908150
-
Can you increase the gas pressure to the valve?
And a silly question, but is all the air out of the gas line?
It takes a long time to purge thru the pilot burner for just seconds at a time.0 -
Clear the pressure switches, tubing, condensate drains.
D0 -
Ok I will try this ... the problem I have is the new gas valve and pilot assembly is doing the same thing as it was when I first arrived on the call so the pressure switch my be the cause I will try blowing the lines out0
-
CORRECTION:
If the pressure switches are NOT satisfied the system usually will not continue in the starting sequence of ignition. IMO
In any case it is good PM to clean hoses and ports on blower.0 -
Can it be possible if the vac switch not opening be caused from the inducer housing cracked I have seen this when the code for vac switches appears.0
-
Yes that's possible, cracks in the drain tubes were also a issue with those. I have also started to see some of those H/E fail. That is a builder grade furnace with aluminum H/E. They are barely making it to the 20 year mark.
D0 -
So that is why I am where I am the whole system runs the ignition starts but no gas for pilot it’s just as of the valve will not see the igniter is lighting0
-
Hmm you should have pilot flame. Did you change out the entire pilot assembly or just the igniter?0
-
I misstated above: If no pressure switch satisfied then ignition sequence would not start...........senior moment typing.
When you have seen the code for vac switches would you get HSI glowing. With that code the control does not see the inducer fan running and should not continue with the sequence. IMO0 -
What are the number s on the Electronic Fan Timer? Is it a Honeywell ST9160? Is the pressure switch a SPDT or a SPST switch?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements