Need help wiring aquastat
Comments
-
-
> @EBEBRATT-Ed said:
> Just turn the aqustat down for now.
>
> I can't tell you how to wire the system without a lot more information. Apparently you plumber needs to call in someone that knows controls
Thanks, Ed. Good idea. I will do that. This guy it totally clueless. I will try and get a photo of how it’s wired now to see if that helps.0 -
> @EBEBRATT-Ed said:
> Just turn the aqustat down for now.
>
> I can't tell you how to wire the system without a lot more information. Apparently you plumber needs to call in someone that knows controls
Ed - just to be clear, the aquastat shouldn’t be checking to see if the boiler is at temp unless the hot water loop is calling for heat, right? Just need a sanity check.0 -
That's correct. The problem may be in the actual placement o the aquastat -- as well as its wiring. If it is in the hot water loop or heat exchanger loop with the pump off, it won't be able to sense the boiler water temperature. It has to be located to sense the boiler water temperature, not the loop temperatures.LongIslandSteamer said:> @EBEBRATT-Ed said:
> Just turn the aqustat down for now.
>
> I can't tell you how to wire the system without a lot more information. Apparently you plumber needs to call in someone that knows controls
Ed - just to be clear, the aquastat shouldn’t be checking to see if the boiler is at temp unless the hot water loop is calling for heat, right? Just need a sanity check.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks Jamie. I am not home to take a picture but the aquastat is a strap on type and it's strapped to the pipe going to the circulator which goes to the heat exchanger. I noticed that the piece of pipe it's strapped to is a small length of iron pipe as opposed to the copper pipe between the circulator and the heat exchanger. Do you think it makes sense to move the aquastat to the length of copper pipe between the circulator and the heat exchanger? I would think copper would be a better medium for conductivity than black iron pipe.Jamie Hall said:
That's correct. The problem may be in the actual placement o the aquastat -- as well as its wiring. If it is in the hot water loop or heat exchanger loop with the pump off, it won't be able to sense the boiler water temperature. It has to be located to sense the boiler water temperature, not the loop temperatures.LongIslandSteamer said:> @EBEBRATT-Ed said:
> Just turn the aqustat down for now.
>
> I can't tell you how to wire the system without a lot more information. Apparently you plumber needs to call in someone that knows controls
Ed - just to be clear, the aquastat shouldn’t be checking to see if the boiler is at temp unless the hot water loop is calling for heat, right? Just need a sanity check.0 -
Problem is that that pipe won't be at boiler temperature unless that circulator is running.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Good point. So i guess the black iron pipe is where it will stay for now. I seemed like it was seated properly when i last looked at it but I wouldnt be surprised if it needs adjustment. Ideally the plumber shouldve installed an aquastat in a well. Having said all that, i think the wiring is the main issue right now.0
-
Jamie - actually now that I thought about it again, the circulator will always be running when the hot water loop zone is calling for heat. that's what should then trigger the aquastat to check the temp on the copper pipe - so i'm thinking the copper is a better place, no?0
-
-
@LongIslandSteamer
not knowing what you have for controls makes it a guessing game.
I would use a two pole relay with NO contacts.
When the thermostat calls for heat (hot water zone) 1 pole starts the HW circulating pump, the other pole goes in series with the aquastat and starts the boiler.
When the stat is satisfied the boiler and pump shut off. When the stat calls the pump and boiler run. The aqustat shuts off the boiler if it gets too hot but will allow the pummp to run to disipate heat as long as the stat is calling
You would be much better off with an imersion aqustat in the boiler and skip the strap on. You don't need an aqustat on the hx or zone piping0 -
Finally got home from work and was able to take a look at my plumber's handiwork. As expected, the aquastat is definitely not wired up correctly. As you can see in the photos, the aquastat is only wired directly to the boiler and has ZERO wires going into the relay.
Is this a simple wiring fix?
0 -
Why is there a jumper between R and W on the SR501?
Edit: disregard. I'm the meatball.0 -
Ah. You do have a relay. @EBEBRATT-Ed 's wiring description is how you want it to go.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I didn't put anything there. I'll tell my plumber to remove it.HVACNUT said:Why is there a jumper between R and W on the SR501? If you didn't put it there to test something temporarily, then remove it ya meatball.
0 -
I just zoomed in and i dont see a jumper. I think it's just the way the wire is laying in the photo.HVACNUT said:Why is there a jumper between R and W on the SR501? If you didn't put it there to test something temporarily, then remove it ya meatball.
0 -
> @LongIslandSteamer said:
> (Quote)
> I just zoomed in and i dont see a jumper. I think it's just the way the wire is laying in the photo.
You're right. Apologies. Maybe it's time to see the optometrist.0 -
@LongIslandSteamer
Discuss with your plumber but this should be acceptable. The L4006A aquastat is a Hi Limit only with an adjustable differential. It will basically act as a cold start.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements